Re: Foam Insulation Spraying

2021-10-12 Thread Fpdcdesign via Sprinklerforum
What jumps out to me is the spray foam insulation. I’m not sure that the requirements for a typical paint spray booth would be applicable. Two very different products. I would look for any research or testing done on that specific product. Also the MSDS for it as a liquid and a

Re: Foam Insulation Spraying

2021-10-12 Thread Skyler Bilbo via Sprinklerforum
See the video below. Fast forward to the spray foam test at about 3 minutes in. Spoiler: flashover takes 44 seconds. Since you are probably acting as the only fire professional on this project, I would suggest you share the video with your customer so they understand the gravity of the

RE: mixing EC sprinks with SC sprinks

2021-10-12 Thread bill.brooks brooksfpe.com via Sprinklerforum
And this seems to be the difference between the Classification of the Occupancy/Commodity (hard part performed by EOR) and figuring out what sprinkler and spacing to use in a particular compartment with clouds, soffits, skylights, beams, joists, hidden spaces, piping configuration, hanger

Foam Insulation Spraying

2021-10-12 Thread David L. Miller, P.E. via Sprinklerforum
Does anyone have advice as to how one would calculate a "spray booth" for spraying foam insulation that is approximately 90' tall X 25' diameter with five levels of working platforms? Typically, when I have done paint booths for vehicles (even as large as fire trucks) I have calculated the

RE: mixing EC sprinks with SC sprinks

2021-10-12 Thread Ed Kramer via Sprinklerforum
I think making the new SC sprinklers standard-response is the best solution in this particular situation. I could see these EC sprinklers being used as both 20'x20' and 14'x14' in the same compartment in order to protect odd-ball areas. Then adding new SC sprinklers and deciding if they should

RE: mixing EC sprinks with SC sprinks

2021-10-12 Thread Taylor Schumacher via Sprinklerforum
We follow how they are listed. If the 3mm bulbs are spaced at SR, we utilize SR 5mm bulbs for adjacent standard coverage sprinklers. Taylor Schumacher -Original Message- From: Sprinklerforum On Behalf Of Mike Morey via Sprinklerforum Sent: Tuesday, October 12, 2021 2:23 PM To:

RE: mixing EC sprinks with SC sprinks

2021-10-12 Thread Mike Morey via Sprinklerforum
I would say if they're all being used as an SR sprinkler based on listing, I would put in SR sprinklers. Is there an AHJ you can lean on? That's what I would approach them with as far as logic. Mike Morey CFPS 3229 * NICET S.E.T. 123677 Project Manager * Fire Protection Group Shambaugh & Son,

mixing EC sprinks with SC sprinks

2021-10-12 Thread Ed Kramer via Sprinklerforum
Forumities, This has likely been previously addressed, but it's just not coming back to me . . . I've got an existing ordinary hazard area that is protected by existing EC sprinklers. The existing EC sprinklers have fast response (3mm) elements and are listed as standard-response for the

RE: Break Tank

2021-10-12 Thread Matt Grise via Sprinklerforum
FM also has some guidance in its data sheets. They are more conservative in their design criteria though. Matt -Original Message- From: Sprinklerforum On Behalf Of John Ammeson via Sprinklerforum Sent: Tuesday, October 12, 2021 6:53 AM To: sprinklerforum@lists.firesprinkler.org Cc:

Re: Break Tank

2021-10-12 Thread John Ammeson via Sprinklerforum
Section 14.5 of NFPA 22. On Tue, Oct 12, 2021 at 6:24 AM Fpdcdesign via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > > > > I have never designed a system with a break tank, however I am working > on one project where this may be a viable option. Is there any good >

Re: Break Tank

2021-10-12 Thread Kevin Hall via Sprinklerforum
I wrote an article on this in the May/June issue of Sprinkler Age: https://issuu.com/sprinklerage/docs/sprinklerage210506/12 In general, minimum 15 minute duration, and then two different refill rates depending if your stored capacity is less than or greater than 30 minutes. On Tue, Oct 12,

Break Tank

2021-10-12 Thread Fpdcdesign via Sprinklerforum
I have never designed a system with a break tank, however I am working on one project where this may be a viable option. Is there any good information one designing a system with one of these? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT