Re: Galvanized underground main

2012-07-30 Thread Jamie.seidl
I believe blaze master is listed for UG, too bad 3 is special order... If you've got the time Greg, CPVC is probably the easiest way to go. Jamie Sent from my iPhone On Jul 30, 2012, at 7:12 PM, Ron Greenman rongreen...@gmail.com wrote: If you follow the gas piping rules you'd use coated

Re: Expansion Joint vs Seismic Joint

2012-03-19 Thread Jamie.seidl
I don't have the standard with me, but expansion joints only require a flex coupling installed (within 2'?). Seismic joints will require the 6 elbow assembly (or equal). I've had architects state that they meant seismic when noting expansion joints on plans before. This promptly turns back

Re: Trash Chute Question

2012-01-04 Thread Jamie.seidl
That sounds more like a wash down sprinkler used to clean the chute. Jamie Sent from my iPhone On Jan 4, 2012, at 2:46 PM, djj8...@aol.com wrote: I had a sprinkler head go off at the top of a trash chute today. The head is in an unreachable position inside the middle the top of the chute.

Re: AP sprinklers

2011-11-18 Thread Jamie.seidl
I believe you will still need to comply with the distances set forth in NFPA. Though I think you get a break for the 10x12 spacing, and not having to comply the 20 psi rule. Someone let me know if I'm way off please, it's been known to happen... Jamie Sent from my iPhone On Nov 18, 2011, at

Re: I-1 sprinklers

2011-09-05 Thread Jamie.seidl
13D for one and two family dwelling units. 13R for multi-family up to 4 stories in height. Jamie Sent from my iPhone On Sep 5, 2011, at 10:09 AM, Todd Williams t...@fpdc.com wrote: Section 903.2.5 of the IBC (2003) states: 903.2.5 Group I. An automatic sprinkler system shall be provided

Re: SMALLEST SPOOL PIECE

2011-07-12 Thread Jamie.seidl
Bet your fab welder a 6 pack he can't do it. I bet it gets done. Jamie Sent from my iPhone On Jul 12, 2011, at 12:39 PM, IPA nsfdc...@gmail.com wrote: Hey Guys, Quick question for guys with field or fabrication experience. What is the smallest spool piece that can be assembled? I need a

Re: CC1/CC2 or COIN sprinklers

2011-06-06 Thread Jamie.seidl
As I understand it the listing is based on UL's 1000 sq ft testing. Your tyco rep should be able to provide more info. Jamie Sent from my iPhone On Jun 6, 2011, at 4:04 PM, Ronl.Fletcher rfletc...@aerofire.com wrote: I wonder if standard SSU's were tested with the 1000 sqft draft stops? Is

Re: IBC and Breezeways

2011-04-06 Thread Jamie.seidl
Ed, it all hinges on what the AHJ considers open and attached. Many jurisdictions don't require breezeways to be sprinklered while some do. It's worth a call to the local and get his 2 cents. Jamie Sent from my iPhone On Apr 6, 2011, at 5:37 PM, Chappell, Carl cchapp...@rjagroup.com wrote:

Re: Dry Sidewalls at back patio

2011-02-21 Thread Jamie.seidl
We've always concealed them in a soffit or perpendicular wall. As long as the insulation is at the exterior wall you'll be fine. Not really sure where he is coming from with that. You are still within the heated envelope of the building. Jamie Sent from my iPhone On Feb 21, 2011, at 5:53

Re: USACE Velocity for Afghanistan work

2010-12-28 Thread Jamie.seidl
Yes there are velocity requirements in the UFC along with the 3000 sqft HMRA. While I don't have them in front of me, 20 or 24 fps comes to mind, and 18 fps at the flow-switch (per UL). This always brings me back to the point of when your calculating the HMRA, wouldn't you also need to calc

Re: USACE Velocity for Afghanistan work

2010-12-28 Thread Jamie.seidl
operates? I would think the later. On Tue, Dec 28, 2010 at 4:49 PM, Jamie.seidl jamie.se...@gmail.com wrote: Yes there are velocity requirements in the UFC along with the 3000 sqft HMRA. While I don't have them in front of me, 20 or 24 fps comes to mind, and 18 fps at the flow-switch (per UL

Re: USACE Velocity for Afghanistan work

2010-12-28 Thread Jamie.seidl
on the switch or a minimum to insure the switch operates? I would think the later. On Tue, Dec 28, 2010 at 4:49 PM, Jamie.seidl jamie.se...@gmail.com wrote: Yes there are velocity requirements in the UFC along with the 3000 sqft HMRA. While I don't have them in front of me, 20 or 24 fps

Concrete tee construction

2010-11-18 Thread Jamie.seidl
Hello forum. Has any one ever encountered 60'+ long concrete tees with an excessive camber? This is a new unloaded parking garage. I am going to contact the engineer of the parking deck, but wanted to run it by the forum first. Thanks again, Jamie Sent from my iPhone

Re: Physical Science :)

2010-11-02 Thread Jamie.seidl
The fire protection handbook. It's all I used. Jamie Sent from my iPhone On Nov 2, 2010, at 5:08 PM, Brian Harris br...@firstdefensefire.com wrote: Any recommendations for good reference material for the Physical Science portion of the Nicet test? Brian Harris First Defense Fire

Re: Physical Science :)

2010-11-02 Thread Jamie.seidl
No, it was one volume, they split it into two in the latest edition. Or was it the second latest? Thank god it was one volume for me... Jamie Sent from my iPhone On Nov 2, 2010, at 7:38 PM, Coastal coastalf...@sc.rr.com wrote: Hello ParsleyConsulting, Half the size of one volume ?

Re: Residential Room Design Method?

2010-10-29 Thread Jamie.seidl
You need to calculate the most hydraulically remote 4 heads. This is typically a loaded branch line that supplies a bedroom on the end of the line. For instance (20x20 * (400 sqft) @ .10 gpm = 40 gpm). This end head pressure will act on the rest of the heads on the BL, closets, bathroom,

Re: Residential Room Design Method?

2010-10-29 Thread Jamie.seidl
See, I really should read the whole email prior to posting. If your full 13, you will still need to be at .10 gpm/sqft per spacing, and if your doing room design, you will still need to pick up 2 sprinklers in the communicating spaces... Not many residential occupancies have rated doors...

Re: Residential Room Design Method?

2010-10-29 Thread Jamie.seidl
the same thing on occasion. Old habits are hard to break, but I try to be cognitive of the fact that every time I use remote I'm inferring something I really don't mean. On Fri, Oct 29, 2010 at 4:46 PM, Jamie.seidl jamie.se...@gmail.com wrote: You need to calculate the most hydraulically

Re: Calcium Chloride antifreeze protection

2010-10-13 Thread Jamie.seidl
I remember the first attic I designed. I drove around for 2 weeks (on my off time) staring at roof slopes, ridges and valleys... It finally began to make sense! Now it just seems like second nature. :) Jamie Sent from my iPhone On Oct 13, 2010, at 7:45 PM, Sprinkler Academy - C Bilbo

Sch 80 pipe

2010-10-08 Thread Jamie.seidl
Does anyone have any information on water filled weight of schedule 80 steel pipe? Jamie Sent from my iPhone ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For

Re: Sch 80 pipe

2010-10-08 Thread Jamie.seidl
68522 Voice (402) 466-2616 Fax (402) 466-2617 da...@mfp-inc.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jamie.seidl Sent: Friday, October 08, 2010 2:05 PM To: Afsa Subject: Sch 80 pipe Does

Re: Type of pump for UG storage tanks

2010-10-08 Thread Jamie.seidl
I've done this on a small remote residential system. The tank was about 8' below the suction flange, so we but a check valve at the tank connection (2- 2500 gal underground rain water storage tanks) put a tee in the suction flange and 4' of riser pipe and a globe valve to prime the suction

Re: Remove me from mailing list please

2010-10-02 Thread Jamie.seidl
Psst, it's at the bottom of every email you've gotten... Jamie Sent from my iPhone On Oct 1, 2010, at 11:09 PM, Un Known sprinkler@gmail.com wrote: Look, I am sorry In the nicest way I say that I can not handle the amount of emails I am getting Can someone please take me off of the

Re: Distance to light fixtures

2010-09-24 Thread Jamie.seidl
I'd stay away from locating a sprinkler above the bar type bathroom lights. They can put out quite a lot of heat, and we all know what goes up... This sounds like a residential fixture, if so, the bulbs may be replaced later with a higher wattage creating more heat. Jamie Sent from my iPhone

Monitor nozzle

2010-09-16 Thread Jamie.seidl
Does anyone have a k factor equivalent for a 1-3/4 monitor nozzle? Jamie Sent from my iPhone ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance,

Re: Monitor nozzle

2010-09-16 Thread Jamie.seidl
Manager Associated Sprinkler Co., LLC 336.373.3901 ext 217 richa...@associatedsprinkler.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jamie.seidl Sent: Thursday, September 16, 2010 9:33 AM

Fire pump meter loop

2010-09-15 Thread Jamie.seidl
I seem to recall that if you have a meter loop on a fire pump, you are still required to install a pump test header, and do a discharge test every 5 years, but I can't seem to find it in 20. Is this correct? Jamie Sent from my iPhone ___

Re: Area Reduction

2010-08-05 Thread Jamie.seidl
Brian, it sounds like an North Carolina state fire marshal spec... If so you won't have a leg to stand on. Don't forget the 25 fps, and 18 fps at the flow switch. Jamie Sent from my iPhone On Aug 5, 2010, at 11:30 AM, Brian Harris br...@firstdefensefire.com wrote: I have an engineer that

Re: siesmic on wood truss

2010-06-15 Thread Jamie.seidl
Is this steel or plastic? Jamie Sent from my iPhone On Jun 15, 2010, at 11:28 AM, Todd Williams t...@fpdc.com wrote: I am working on an apartment building with wood truss floor assemblies. The trusses are 2x4s on their side (1-1/2 end vertical) I need to find an attachment to connect the

Re: siesmic on wood truss

2010-06-15 Thread Jamie.seidl
For the standpipe I would talk with the truss designer. You'll probably need to add 2x blocking at a certain span to meet the load requirements for the bracing, just like you would for the hangers. He may also have to add bridging on his end. As for the CPVC, it's basically braced

Re: 3/4 pipe

2010-06-14 Thread Jamie.seidl
3/4 is allowed in non-ferrous materials. Jamie Sent from my iPhone On Jun 14, 2010, at 4:07 PM, James Zimmerman zimm...@gmail.com wrote: I have a specification that states nothing less than 1 pipe shall be used for a sprinkler system. Is there anywhere in NFPA 13 that prohibits the use

Re: Pressure Reducing Valve Info.

2010-06-07 Thread Jamie.seidl
Try www.giacomini.com/en/systems/fire_protection/catalouges_and_documentation/ Jamie Sent from my iPhone On Jun 7, 2010, at 3:35 PM, lamarvau...@charter.net wrote: Good Afternoon Forumites, I am looking for technical data on a 2.5 Giacomini Pressure Reducing valve . I have tried

Re: Mixing QR and SR Heads

2010-06-04 Thread Jamie.seidl
I think the issue of QR/SR listing difference on EC heads is the fact that try want to exclude the use of a reduce design area in ordinary hazard occupancy when utilizing EC heads. That's why it's QR at 14'x14' and SR at 16'x16'. It's still a QR bulb, but you don't get the area reduction

Re: SprinkCAD vs HydraCAD

2010-06-02 Thread Jamie.seidl
Yep, simple hydraulic calculator is a great program. Simple, clean and the input really reminds of me of the old sigma hydraulic program (without having to drop to DOS ofcourse). Jamie Sent from my iPhone On Jun 2, 2010, at 9:41 PM, Trevor Spain supp...@igneusinc.com wrote: For those who

Re: Elevator Equipment Rooms

2010-05-24 Thread Jamie.seidl
That's been pretty typical in NC for awhile. Also electrical rooms. Jamie Sent from my iPhone On May 24, 2010, at 10:00 AM, Brian Harris br...@firstdefensefire.com wrote: Good Morning Gents: Quick question regarding Elevator Equipment Rooms: is it permissible for a sprinkler line to