[Sprinklerforum] Re: Air venting

2023-10-10 Thread Taylor Schumacher
Schumacher Security Fire Sprinkler<http://www.j-berd.com/> 1 Industrial Blvd | Sauk Rapids, MN 56379 Office: 320.656.0847 | Direct: 320.640.7050 From: Ken Wagoner Sent: Tuesday, October 10, 2023 4:05 PM To: sprinklerforum@lists.firesprinkler.org Subject: [Sprinklerforum] Re: Air venting C

[Sprinklerforum] Re: Air venting

2023-10-10 Thread Ken Wagoner
9 *matthew.will...@ferguson.com <mailto:matthew.will...@ferguson.com>* *www.FergusonFire.com <http://www.fergusonfire.com/>* *From:* Ken Wagoner *Sent:* Monday, October 9, 2023 7:26 PM *To:* sprinklerforum@lists.firesprinkler.org *Subject:* [Sprinklerforum] Re: Air venting I understand and agree T

[Sprinklerforum] Re: Air venting

2023-10-10 Thread matthew.willis1
ill...@ferguson.com> www.FergusonFire.com<http://www.fergusonfire.com/> From: Ken Wagoner Sent: Monday, October 9, 2023 7:26 PM To: sprinklerforum@lists.firesprinkler.org Subject: [Sprinklerforum] Re: Air venting I understand and agree Todd, before I shot my mouth of to the layout tech I want

[Sprinklerforum] Re: Air venting

2023-10-09 Thread Taylor Schumacher
It sounds like an apartment building. If the floors above are CPVC systems, they wouldn’t require an air vent. I would argue the use of metal devices in the valve assembly does not constitute a metallic pipe system. Taylor Schumacher Security Fire Sprinkler 1

[Sprinklerforum] Re: Air venting

2023-10-09 Thread Ken Wagoner
It is even more of an issue for this building, as the only air vent valve is provided on the garage level of a four story building. thank you all for the good and timely responses, *Ken Wagoner, SET* *Parsley Consulting 500 West Mechanic Street Harrisonville, Missouri 64701-2235* *Phone: (760)

[Sprinklerforum] Re: Air venting

2023-10-09 Thread Ken Wagoner
I understand and agree Todd, before I shot my mouth of to the layout tech I wanted to make sure I was headed in the right direction. Thank you! *Ken Wagoner, SET* *Parsley Consulting 500 West Mechanic Street Harrisonville, Missouri 64701-2235* *Phone: (760) 745-6181 * *Visit the website

[Sprinklerforum] Re: Air venting

2023-10-09 Thread Ron Greenman
.will...@ferguson.com * > > *www.FergusonFire.com <http://www.fergusonfire.com/>* > > > > > > *From:* John Denhardt > *Sent:* Monday, October 9, 2023 12:35 PM > *To:* Discussion list on issues relating to automatic fire sprinklers < > sprinklerforum@lists.fires

[Sprinklerforum] Re: Air venting

2023-10-09 Thread matthew.willis1
sonFire.com<http://www.fergusonfire.com/> From: John Denhardt Sent: Monday, October 9, 2023 12:35 PM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: Air venting The language in NFPA 13 is clear from my perspective. One air release per

[Sprinklerforum] Re: Air venting

2023-10-09 Thread Mike Morey
atic fire sprinklers Subject: [Sprinklerforum] Re: Air venting Ken, I think you would have to with the check valve. I would push back a little in that by adding a normally open valve and a flow switch or manifold would not change the physics of the system enough to warrant the additional v

[Sprinklerforum] Re: Air venting

2023-10-09 Thread John Denhardt
The language in NFPA 13 is clear from my perspective.  One air release per wet sprinkler system.For example - A 50 story building with one wet sprinkler zone control assembly per floor would require 50 air release valves. JohnJohn August Denhardt, P.E.Vice-President Engineering and Technical

[Sprinklerforum] Re: Air venting

2023-10-09 Thread Hinson, Ryan
Hey Ken, As has already been stated by others, I believe the intent is to remove as much air from 'each wet system' as possible. 'System', in this case, is any piping network isolated from the rest of the upstream system by isolation valving be it a check valve or a shutoff valve. Support for

[Sprinklerforum] Re: Air venting

2023-10-09 Thread Anthony Carrizosa
: Fpdcdesign Sent: Monday, October 9, 2023 9:28 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: Air venting Ken, I think you would have to with the check valve. I would push back a little in that by adding a normally open valve and a flow

[Sprinklerforum] Re: Air venting

2023-10-09 Thread Fpdcdesign
Ken, I think you would have to with the check valve. I would push back a little in that by adding a normally open valve and a flow switch or manifold would not change the physics of the system enough to warrant the additional vents. If you had a 2 story building without zone valves,

[Sprinklerforum] Re: Air venting

2023-10-09 Thread Anthony Carrizosa
Ken The Appendix states that it is necessary to choose a location where the greatest volume of trapped air is vented during the first fill and each subsequent drain and fill event. Being that you must have a control valve, water flow alarm and drain for each floor then that is the definition of

[Sprinklerforum] Re: Air venting

2023-10-09 Thread Taylor Schumacher
From: Ken Wagoner Sent: Monday, October 09, 2023 11:05 AM To: sprinklerforum@lists.firesprinkler.org Subject: [Sprinklerforum] Re: Air venting Caution: This email originated from outside your organization. Please take care when clicking links or opening attachments. Yes, Todd, on each

[Sprinklerforum] Re: Air venting

2023-10-09 Thread Ken Wagoner
Yes, Todd, on each floor, as they're using a Victaulic UMC manifold which includes a check valve. thanks for the information, *Ken Wagoner, SET* *Parsley Consulting 500 West Mechanic Street Harrisonville, Missouri 64701-2235* *Phone: (760) 745-6181 * *Visit the website

[Sprinklerforum] Re: Air venting

2023-10-09 Thread matthew.willis1
ber 9, 2023 11:51 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: Air venting My understanding is that it is per system. Travis Mack, SET M.E.P.CAD | Instructor / Support 181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074 www.mepcad.com&l

[Sprinklerforum] Re: Air venting

2023-10-09 Thread Travis Mack
My understanding is that it is per system. Travis Mack, SET M.E.P.CAD | Instructor / Support 181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074 www.mepcad.com | m: 480.547.9348| Whatspp: +14805479348 Email: t.m...@mepcad.com AutoSPRINK | AutoSPRINK FAB |

[Sprinklerforum] Re: Air venting

2023-10-09 Thread Dale Wingard
Ken, I would say that you are correct that each floor is a separate sprinkler system and will require it’s own means of venting. Regards, Dale F. Wingard, SET Designer Commercial/Marine Division NICET IV #76284 Water-based Systems 3751 Joy Springs Drive, Mobile, Alabama 36693 o: 251.661.1275

[Sprinklerforum] Re: Air venting

2023-10-09 Thread Fpdcdesign
Is there a check valve on the floor control assembly? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (tel:860-535-2080) (ofc) 860-554-7054 (tel:860-554-7054) (fax) 860-608-4559 (tel:860-608-4559) (cell) > > On Oct 9,

[Sprinklerforum] Re: Air venting

2023-10-09 Thread matthew.willis1
You are correct. The air vent is required on each wet pipe system. If we look at the definitions in chapter 3, you have separate systems each floor. R/ Matt Please rate our customer service Matthew J. Willis, CWBSP,