[Sprinklerforum] Re: ESFR Addition

2022-10-12 Thread Ron Greenman
Is this new addition a "proper" separate building or just another fire area. If the former your solution of a booster pump for just the EFSR "building" tapped from the main UG line sounds like a good solution. If just a fire area Ken's comment about FDC feeds after the pump is spot on. I'd also thi

[Sprinklerforum] Re: ESFR Addition

2022-10-12 Thread Ken Wagoner
Bobby, Yes, I now understand what you're describing, and your description clarified it a great deal. I'm in agreement with Travis on this one, there's no mandate that all four risers have to be fed by the pump discharge, and as was pointed out providing an separate pump for each riser would

[Sprinklerforum] Re: ESFR Addition

2022-10-12 Thread Rick Matsuda
October 12, 2022 10:40 AM > To: Ken Wagoner ; Discussion list on issues > relating to automatic fire sprinklers > Subject: [Sprinklerforum] Re: ESFR Addition > > No there is no existing fire pump the existing risers are feed from the city > water supply. There is a new addition b

[Sprinklerforum] Re: ESFR Addition

2022-10-12 Thread Travis.Mack
To: Ken Wagoner ; Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: ESFR Addition No there is no existing fire pump the existing risers are feed from the city water supply. There is a new addition being added to the building which requires a ESFR system m

[Sprinklerforum] Re: ESFR Addition

2022-10-12 Thread Bobby Welch
No there is no existing fire pump the existing risers are feed from the city water supply. There is a new addition being added to the building which requires a ESFR system my question was is there a code that does not allow me to tie in to the bottom of one of the existing risers to feed a new f

[Sprinklerforum] Re: ESFR Addition

2022-10-12 Thread Ken Wagoner
Bobby, I have to admit I'm sort of baffled here. If I read this correctly, the discharge flow and pressure from the _*existing*_ fire pump will not supply sufficient flow and pressure to the base of the new riser, as required by the K16.8 ESFR sprinklers. So your thinking is to provide tap t

[Sprinklerforum] Re: ESFR Addition

2022-10-11 Thread Kyle . Montgomery
In this scenario, would the FDC be pressurizing the suction side of the fire pump? You are usually not supposed to do that. Kyle Montgomery [cid:image001.png@01D8DD6E.36E83BC0] Aero Automatic Sprinkler Co. 21605 N. Central Ave. Phoenix, AZ 85024 Direct: 623.580.7820 Cell: 602.763.4736 kmontgom..