contaminating the potable water?
Whatever you do, keep us posted on what worked.
-Kyle M
From: Joe Burtell
Sent: Thursday, August 26, 2021 8:46 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Kyle.Montgomery ; Prahl, Craig/GVL
; Matt Grise
Subject: [EXTERNAL] Re: Fire Pump Backflow
This is a real
that), I'd appreciate a
> lesson in the physics of how/why?
>
> -Kyle M
>
>
> -Original Message-
> From: Sprinklerforum On
> Behalf Of Prahl, Craig/GVL via Sprinklerforum
> Sent: Thursday, August 26, 2021 5:44 AM
> To: sprinklerforum@lists.firesprinkler.org
M
To: sprinklerforum@lists.firesprinkler.org
Cc: Prahl, Craig/GVL ; Matt Grise
Subject: [EXTERNAL] RE: Fire Pump Backflow
I have doubts that the "engineer" has any clue what a jockey pump does or how
it works.
So, you'd have a connection on the suction side of the fire pump that typically
con
g
Cc: Matt Grise
Subject: [EXTERNAL] RE: Fire Pump Backflow
For the jockey piping - I wonder if the engineer meant to say that you could
pressurize the portion of the piping between the backflow preventer and the
fire pump with the jockey pump. Maybe have an additional check valve after the
BFP, but b
has the budget for a break tank?
Matt
-Original Message-
From: Sprinklerforum On Behalf
Of Skyler Bilbo via Sprinklerforum
Sent: Wednesday, August 25, 2021 8:09 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Skyler Bilbo
Subject: Re: Fire Pump Backflow
I never had this problem before,
r
> > > systems being fed from the same tanks that would necessitate the BFP?
> > >
> > > Cliff Whitfield, SET
> > > President
> > >
> > > Fire Design, Inc.
> > > 940 Summerbrooke Drive
> > > Tallahassee, FL 32312
> > > P
ame tanks that would necessitate the BFP?
> >
> > Cliff Whitfield, SET
> > President
> >
> > Fire Design, Inc.
> > 940 Summerbrooke Drive
> > Tallahassee, FL 32312
> > Ph: 828-284-4772
> >
> >
> >
> > cl...@fire-design.com
> > ww
gt; Ph: 828-284-4772
>>
>>
>>
>> cl...@fire-design.com
>> www.fire-design.com
>>
>> -Original Message-
>> From: Sprinklerforum On
>> Behalf Of Joe Burtell via Sprinklerforum
>> Sent: Wednesday, August 25, 2021 3:33 PM
>> To: sprinklerf
forum On Behalf
Of Joe Burtell via Sprinklerforum
Sent: Wednesday, August 25, 2021 3:33 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Joe Burtell
Subject: [EXTERNAL] Fire Pump Backflow
I have a situation with a verticle in-line fire pump fed from water storage
tanks. We have a double check bac
; Ph: 828-284-4772
>
>
>
> cl...@fire-design.com
> www.fire-design.com
>
> -Original Message-
> From: Sprinklerforum On
> Behalf Of Joe Burtell via Sprinklerforum
> Sent: Wednesday, August 25, 2021 3:33 PM
> To: sprinklerforum@lists.firesprinkler.org
> Cc:
5, 2021 3:33 PM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Joe Burtell
> Subject: Fire Pump Backflow
>
> I have a situation with a verticle in-line fire pump fed from water
> storage tanks. We have a double check backflow installed between the tanks
> and the fire pump
-design.com
-Original Message-
From: Sprinklerforum On Behalf
Of Joe Burtell via Sprinklerforum
Sent: Wednesday, August 25, 2021 3:33 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Joe Burtell
Subject: Fire Pump Backflow
I have a situation with a verticle in-line fire pump fed from
esday, August 25, 2021 3:33 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Joe Burtell
Subject: Fire Pump Backflow
BE ADVISED - This email originated outside EMCOR.
I have a situation with a verticle in-line fire pump fed from water storage
tanks. We have a double check backflow install
I have a situation with a verticle in-line fire pump fed from water
storage tanks. We have a double check backflow installed between the tanks
and the fire pump but we don't have enough pressure to open the backflow on
the upstream side between the tank and backflow. I talked with Watts about
it. T