RE: Fire Protection System for Cleanroom and NMR

2009-03-20 Thread Geir Jensen
Pre-action makes most sense to me as well. That is, when goal is to prevent fire spread to other rooms by fire starting in such vital room. Pre-action is not really statistically justified to avoid unintentional water application and wet sprinkler is more reliable in performing on demand in a

RE: Fire Pump relief valve discharge

2009-03-20 Thread lamarvaughn
The practice of connecting the relief valve discharge to the pump suction has been accepted for many years.It was removed from NFPA #20 in the nineties but has since been reinstated.I have done this many times for many reasons without any problems.Because it is a closed loop,I have not increased

RE: Fire Pump relief valve discharge

2009-03-20 Thread rahe . loftin
Any problem dumping the relief discharge back into the tank? Thank You Rahe Loftin, P.E. Region 7 - GSA Office - 817-978-7299 Fax - 817-978-8644 Cell - 817-371-3102 ___ Sprinklerforum mailing list

RE: Fire Pump relief valve discharge

2009-03-20 Thread Tom Duross
If the relief valve is installed before the pump check, it's going to effect your numbers a little when you test. IMHO, the BEST way to pipe it is as Rahe suggests that way you have a break and tank circulation (which is a good thing for weekly's). I assume no bypass but will you have a flowmeter

RE: Fire Pump relief valve discharge

2009-03-20 Thread Todd Williams
No. Follow the same rules as you would for discharging a flow meter back into a tank. At 09:16 AM 3/20/2009, you wrote: Any problem dumping the relief discharge back into the tank? Thank You Rahe Loftin, P.E. Region 7 - GSA Office - 817-978-7299 Fax - 817-978-8644 Cell - 817-371-3102

IRC in Colorado

2009-03-20 Thread Ron Greenman
Does anyone out therte know what the trade-offs Pat is referring to in the below memo are? Hello All: Given the initiatives in some states to forestall the adoption of the IRC in order to eliminate sprinkler requirements in new 1 2-family homes, I wanted to let you know that there

RE: Fire Pump relief valve discharge

2009-03-20 Thread George Church
Other than the turbulence, which was deemed acceptable for the condition where the relief is piped back to suction under #20, the pipe running from the tank to the suction side of the pump is the same chamber as the tank- unless there's a OSY right on the suction nozzle of the tank- and if you're

RE: Excessive system pressure

2009-03-20 Thread Rodney Hamm
Yes we have many dry systems. I have never seen one which does not have a pressure regulator and an adjustable PRV. Most of the adjustable PRV's are set to relieve any pressure which is 10-15 psi above the set pressure. Rodney K. Hamm, P.E. President/Owner Falcon Fire Protection Office (478)

Excessive system pressure

2009-03-20 Thread Rodney Hamm
Wow what a week..I was at another plant yesterday which has the same exact problem. This facility has 14 wet systems fed by a fire pump so the static pressure is maintained by a jockey pump at 170 psi. Several systems had system pressures 175 psi. One of the gridded systems had a system pressure

RE: Excessive system pressure

2009-03-20 Thread Craig.Prahl
Does the plant realize that once all your air is gone that these prv's will be dribbling water every time the system warms up? Hopefully they have a good mop-up crew. Air is the cushion in the system, systems will over pressurize once they have become water logged and there is no place for

RE: Excessive system pressure

2009-03-20 Thread Rodney Hamm
I FULLY INTEND THAT THIS WILL BE MY LAST POST REGARDING THIS SUBJECT. I promise to make a concerted effort to make this statement true. I would also like to state that you should probably read this entire post if you have not completely tuned out regarding this subject! I obtained my Bachelors

RE: Excessive system pressure

2009-03-20 Thread Craig.Prahl
No branding here. Everyone enjoys a spirited discussion now and then. Keeps the viewer ratings up. lol Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax -

Re: Excessive system pressure

2009-03-20 Thread Trevor Spain
Rodney, Last week when I posted on the incompressibility of pure water (14.7 psi to reduce volume 1 part in 5x10^7) illustrated through a hypothetical temperature swing from 40F to 80F, I thought my statement of BIG PRESSURE was self explanatory on the massive pressure increase water can

RE: Fire Pump relief valve discharge

2009-03-20 Thread A.P.Silva
Yes. This building is in an area up north where the temperature drops to -40 to -50 deg.C in the winter. The suction pipe from gravity tanks to pumphouse is heat traced and isulated. Running relief discharge to tank will be a big cost. The flow meter runs back to the tank,bu it is too small to

Re: Fire Pump relief valve discharge

2009-03-20 Thread Roland Huggins
How about a more basic question. Why do you even have a relief valve? With a rating of only 105 psi exceeding 175 psi with a tank feed requires a tall tank. Roland On Mar 19, 2009, at 11:23 PM, A.P.Silva wrote: The building owner wants to connect the discharge piping from the pump

Re: Fire Pump relief valve discharge

2009-03-20 Thread Rodney Hamm
Tony made reference to a 4 in. diameter PRV, so I assume he is dealing with a diesel driven fire pump. The PRV is required for all diesel driven fire pumps. If the diesel driver rpm increases higher than the set idle position, the system pressure could easily exceed 175 psi without a suitable PRV.

Re: air pockets and false alarms (aka: Statistics)

2009-03-20 Thread Jim . Roberts
I had not been following the thread because the subject title hasn't changed, but am I correct in assuming this problem does not occur with pressure switches at the top of retard chambers? James L.(Jim) Roberts, PE/SET Fluor Corporation 100 Fluor Daniel Drive - C104F Greenville, SC 29607

RE: Fire Pump relief valve discharge

2009-03-20 Thread A.P.Silva
True. Good point. I should've mentioned the pump is diesel. The tank is 40' high. To conform to NFPA 20, 2007 section 5.18.1.1, 121% of churn gives (105 x 120% x 121%) + (40 x .433) = 170 psi (approx), assuming churn pressure is 120% of rated pressure. Someone would have thought it was not too

RE: Fire Pump relief valve discharge

2009-03-20 Thread A.P.Silva
Thanks. A waste cone and sight glass are included. Tony -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Rodney Hamm Sent: March 20, 2009 10:26 AM To: sprinklerforum@firesprinkler.org Subject: Re: Fire Pump

Re: Fire Pump relief valve discharge

2009-03-20 Thread Roland Huggins
If it is a relatively new pump, it may churn at 140% but I'd be shocked if that were the case. I haven't gone looking but has any one seen a horizontal pump that exceeds the old 120% criteria? The pumps I've played with have been less than 110% and there are a boat load that are at or

Re: air pockets and false alarms (aka: Statistics)

2009-03-20 Thread Ed Vining
Yes Jim. Pressure in the retard chamber is relieved through the drain when the alarm port is closed. On Fri, Mar 20, 2009 at 10:26 AM, jim.robe...@fluor.com wrote: I had not been following the thread because the subject title hasn't changed, but am I correct in assuming this problem does not

RE: IRC in Colorado

2009-03-20 Thread Thom McMahon
Ron: I checked with the Colorado Div. of Fire Safety, and no decisions have been made on code adoptions Steve Gasowski of the Div. said he's part of an Ad Hock committee reviewing this and other code adoption issues, but no final decisions yet. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge

RE: Excessive system pressure

2009-03-20 Thread Michael Fitz
, P.E. President/Owner Falcon Fire Protection Office (478) 953-1677 Cell (478) 396-6988 __ Information from ESET Smart Security, version of virus signature database 3952 (20090320) __ The message was checked by ESET Smart Security. http://www.eset.com

RE: Excessive system pressure

2009-03-20 Thread bill . brooks
Rodney, You said you aren't hard headed and you understand the principles behind the system pressure increases. Here's a chance to prove both. 1. Two containers of identical volume. One container 50% water, the other container 100% water. Each has been sitting in a 50 F room with the lid

RE: Excessive system pressure

2009-03-20 Thread Michael Fitz