RE: Slow responding dry pipe valves

2009-06-17 Thread Damien Shannon
Frans, Very curious to know how you got on with the Victaulic valve w/ 1300 gallons to make the 60 sec requirement after making the adjustments discussed (or anywhere close). I need to do a building with 8 dry systems (new construction) that requires all the valves at a main header. The bulk main

RE: convention

2009-06-17 Thread George Church
Due to an unanticipated delay in delivery of its 2009 convention brochure, AFSA is extending the early bird registration deadline by one week to Friday, July 17 to allow everyone ample opportunity to save! Also, be sure to follow AFSA on Twitter at http://www.twitter.com/afsa to save even more

Temperature Rating

2009-06-17 Thread Chris Cahill
'07 8.3.2 Rating and 8.3.3 Sensitivity I can find no place where is says what if anything should be done with different ratings in the same room (10,000 sq. ft. ish room). 8.3.3 clearly says when QR all in compartment must be QR. But in the temperature rating there is nothing like that.

RE: Slow responding dry pipe valves

2009-06-17 Thread George Church
Damien- I'd highly recommend you: 1. Read James G's white paper Variables that affect the Performance of Dry Pipe Systems at http://www.tyco-fire.com/index.php?P=showid=DryPipeSystems_RevB=BK=archiv e_news 2. Look into obtaining FDT calculation software to either prove your systems' ability to

RE: Slow responding dry pipe valves - FDT

2009-06-17 Thread Chris Cahill
Anyone done some field testing out of curiosity on real systems you've installed and compared the results of FDT vs. real world. I did once about 6 years ago and FDT and real world were 45 sec. vs. 70 sec. respectively. Raised questions but with a test of one no conclusions. Haven't been

RE: Temperature Rating

2009-06-17 Thread Thom McMahon
NFPA 13 2007 sets a min. temp for OH of 150'F but no maximum except to say intermediate or high temp are both ok. Notes: see 8.3.2.3 , 8.3.2.7 , 8.3.3.2 , A8.4 , 8.4.7.3.3 Maybe have the AHJ show where it prohibits have the two temps adjacent? Put a heater in a 165'f protected space and you could

RE: Slow responding dry pipe valves - FDT

2009-06-17 Thread Travis Mack
I did a couple of preaction systems about 3 years ago. The FDT and field tests were within 1-2 secs if I recall correctly. I was pretty impressed. We did have a fire pump and tank on the project, so there would not have been any variability from a city supply. The systems were large (+/-1200

RE: Slow responding dry pipe valves

2009-06-17 Thread Brown, Mike
But what happens when then software shows the system tripping in the required amount of time...then when it comes time for final inspection with the AHJ and it doesn't work? That could be costly mistake !? Mike Brown Designer Sunland Fire Protection 1218 Elon Place High Point, NC 27263 Ph.

RE: Temperature Rating

2009-06-17 Thread Craig.Prahl
Question is, why two different temp ratings in the same common space? Also if this is a warehouse and it's non-conditioned, what is the max. indoor temperature this area could experience? 165's might be a bit low? Craig L. Prahl, CET Fire Protection Specialist Mechanical Department

RE: Temperature Rating

2009-06-17 Thread Chris Cahill
Don't know, many changes of occupancies/occupants over the years. Perhaps there was a wall at some time that is gone. Perhaps the 165's were over a combustible office that is long gone. Perhaps the original installers ran out of 286's and didn't want to order more. Today I don't see the why as

RE: Slow responding dry pipe valves

2009-06-17 Thread Chris Cahill
Code is clear - FDT supersedes real life if there is a discrepancy '02-7.2.3.3 and 11.2.3.9. Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: chr...@sentryfiremn.com Mail: P.O. Box 69 Waverly, MN 55390 Location: 4439

Gymnasium

2009-06-17 Thread ETHER BARLOW
Are Sprinklers required in a Gymnasium with a deck height of 50 ft, noncombustible construction? -- My Thanks to You! Ether J. Barlow Cell 702-375-1228 ___ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For

RE: Gymnasium

2009-06-17 Thread Arthur Tiroly
Is it in a public school? Is the school required to have sprinklers? Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 3300 King Ave Cleveland, OH 44114 216-621-8899 216-570-7030 cell -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Gymnasium

2009-06-17 Thread Reed Roisum
Need more info... What code applies? What is the occupancy classification? Is there spectator seating? What is the square footage? Occupant load? Is it on a the floor level of exit discharge? Reed A. Roisum, CET Fire Protection Technician Ulteig Engineers, Inc. 3350 38th Avenue South

RE: Slow responding dry pipe valves-FDT

2009-06-17 Thread Brown, Mike
I don't doubt what everyone is saying... I understand the code as Chris stated... I'm thinking about from some of our local AHJ's perspective. I have a feeling that some of the old school AHJ's could care less about what the software says and are more concerned with real life results. Mike Brown

Re: Gymnasium

2009-06-17 Thread ETHER BARLOW
9900 sqft 02' NFPA13, Bleachers on one side, Ground Level, OH1? Probably about 150 people. On Wed, Jun 17, 2009 at 12:17 PM, Reed Roisum reed.roi...@ulteig.comwrote: Need more info... What code applies? What is the occupancy classification? Is there spectator seating? What is the square

RE: Slow responding dry pipe valves-FDT

2009-06-17 Thread Chris Cahill
Do these same AHJ's make you do a remote area density flow test, live water on the floor? It really is the same thing. Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: chr...@sentryfiremn.com Mail: P.O. Box 69 Waverly,

RE: Slow responding dry pipe valves-FDT

2009-06-17 Thread Chris Cahill
Let me clarify, I thought it was way too far off in the 1 example I was involved with. 45 sec. calc after it repeatedly failed in the real world at any place between 70 sec and 80 seconds. The contractor used it after the fact when they failed the 60 second test on at least 3 occasions. Tyco

RE: Gymnasium

2009-06-17 Thread Reed Roisum
Ether, I was referring to IBC occupancy classifications. This would most likely be an A-4 occupancy (assuming IBC). A-4 occupancies require and automatic sprinkler system if the fire area exceeds 12,000 sq. ft, the occupant load is over 300, or the fire area is on a floor other than the

Re: Slow responding dry pipe valves - FDT

2009-06-17 Thread Roland Huggins
There was a change in the 13 ROP that addresses this issue. It points out that even when water delivery is calculated, the acceptance test still requires a timed delivery for future ITM. It states that if a single outlet takes longer than 70 sec then it must be evaluated. To be honest,

RE: Gymnasium

2009-06-17 Thread Todd Williams
Schools tend to use gymnasiums for storage during to off season. At 03:17 PM 6/17/2009, you wrote: Need more info... What code applies? What is the occupancy classification? Is there spectator seating? What is the square footage? Occupant load? Is it on a the floor level of exit

RE: Slow responding dry pipe valves-FDT

2009-06-17 Thread Ken Holsopple (forum)
Chris wrote: Let me clarify, I thought it was way too far off in the 1 example I was involved with. 45 sec. calc after it repeatedly failed in the real world at any place between 70 sec and 80 seconds. The contractor used it after the fact when they failed the 60 second test on at least 3

RE: Slow responding dry pipe valves-FDT

2009-06-17 Thread George Church
To address Mike's concern about trip time, the QRS switch is pretty dependable- it samples the air pressure every .1 seconds and after enough degradation is detected 3x in a row, it trips. We input 3.5 second trip time even tho it would be a little less since it takes less than a .5 second to trip

RE: Slow responding dry pipe valves

2009-06-17 Thread George Church
Slow to respond isn't so bad. We've been having problems with not just SLOW to respond, we're having NOOOooo response to loss of air pressure. On a freeze up last winter, one didn't trip and that was sort of a good thing, avoided water damage. But when a maintenance man watches my inspector let

RE: Gymnasium

2009-06-17 Thread Thom McMahon
Very rare that a school gym won't have an occupant load of 300. I was in our middle school gym last week with 6 or 700 friends and families of the 8th grade class, plus the students teachers, and administrators. Our gym is less than 10,000 sf.(Oh and did I forget the 6th 7th grade band was there

I'm embarrassed to be an AHJ(The Chief's thinking is disturbing)

2009-06-17 Thread Thomas Reinhardt
The message is ready to be sent with the following file or link attachments: Shortcut to: http://www.tennessean.com/article/20090615/COUNTY090101/906150306/1327/Fire+chief+opposes+proposed+sprinkler+law Note: To protect against computer viruses, e-mail programs may prevent sending or

Re: Metal building

2009-06-17 Thread Todd Williams
From you description, it appears not. However, I wouldn't remove the existing, just add to it. At 05:38 PM 6/17/2009, you wrote: Hello Everyone. There is a metal building(23-0 Floor to deck), open floor plan. Standard uprights in there now. A drop ceiling is going to be put in at 10'-0.

RE: Metal building

2009-06-17 Thread Cliff Whitfield
Nick, It has always been my belief that unless there was some reason to remove an existing system, I always leave it in place. Naturally there are some instances that would require removal but many times they are fine left in place.If you leave them, this owner may one day sell the bldg and

Re: Metal building

2009-06-17 Thread Nick Melosi
Thanks guys. On Wed, Jun 17, 2009 at 4:51 PM, Cliff Whitfield cl...@fire-design.comwrote: Nick, It has always been my belief that unless there was some reason to remove an existing system, I always leave it in place. Naturally there are some instances that would require removal but many

RE: Metal building

2009-06-17 Thread Phelps, Mark
The need for sprinklers above the ceiling is determined by the building code classification of the building. Even though there are no combustibles above the ceiling now, there may be if it is a Type III B, Va or Vb. Many AHJ's require sprinklers in a concealed space based on the building code

Re: Slow responding dry pipe valves-FDT

2009-06-17 Thread Ron Greenman
So what drove the change from the old way of working trip times (under 500 gal. all was good, 500-750 gals. and either 60 seconds or QOD, over 750 gals. QOD and all is good)? was it due to systems failing due to too long trip times or was it a way to sell an expensive computer program? If due to

Re: Slow responding dry pipe valves-FDT

2009-06-17 Thread Roland Huggins
nothing changed (except for dwelling units). The 500 gal w/o QOD or 750 gal limits still apply. The timed approach is just for exceeding them. As for dwelling units, it is not 15 sec regardless of size. Roland On Jun 17, 2009, at 3:44 PM, Ron Greenman wrote: So what drove the change

Re: Slow responding dry pipe valves-FDT

2009-06-17 Thread Ron Greenman
As I read this it seems to say that the same rules apply as before but to prove the system size I have to use an approved computer program. Now I'm no math whiz but I can calculate the capacity of a bunch of tubes (pie is square times length equals cubic X, convert X cubes to cubic feet, convert

Re: Slow responding dry pipe valves-FDT

2009-06-17 Thread Todd Williams
Could it have something to do with the fact that the multi-thousand dollar program is UL listed and your smelly feet aren't? At 07:19 PM 6/17/2009, you wrote: As I read this it seems to say that the same rules apply as before but to prove the system size I have to use an approved computer

Re: I'm embarrassed to be an AHJ(The Chief's thinking is disturbing)

2009-06-17 Thread Jay Jay Blocker
Another part of the story.   I wonder if he is taking a little heat for his decision.  My question is how can the contractor go over the local AHJ to the state?  Isnt the local AHJ the one to deal with? Tenn. Chief Defends Code Stance Jun 16, 2009 5:35 PM By Janet Wilmoth Would a fire chief

RE: Slow responding dry pipe valves-FDT

2009-06-17 Thread George Church
Because if its not computer-generated output, it can't be right. glc -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman SNIP Time consuming but why do I need a multi-thousand dollar program for a

RE: Slow responding dry pipe valves-FDT

2009-06-17 Thread Todd Williams
George, I believe that the 52000 sqft came from 400 sprinklers x 130 sqft per sprinkler. The 400 someone probably pulled out of a body orifice. If you want to pick nits, sprinklers discharge water in a circle and we calculate them in a square. How come we don't have circular remote areas? Do

RE: Slow responding dry pipe valves-FDT

2009-06-17 Thread Jim Johnston
Ron, I haven't been following this too close (been actually doing some work) the software is meant to calc the water delivery time not necessarily the volume as I think you are thinking although it needs this? From what I understand Tyco did a great job at selling this to the 13 committee. From

Re: Slow responding dry pipe valves-FDT

2009-06-17 Thread Ron Greenman
Jim, Goes back to my original question of how come we need to do this now when before all we needed to do was a little geometry to demonstrate size in gallons, do nothing extraordinary in the system was less than 500 gallons, put on a QOD if above 750 and show 60 seconds or less or put on a QOD

Re: I'm embarrassed to be an AHJ(The Chief's thinking is disturbing)

2009-06-17 Thread J. Scott Mitchell
Why even have local requirements if you're always going to go with what the state requires?  The show prep meetings would be the shortest ever and the ordinance would be one sentence long. J. Scott Mitchell, P.E. From: Thomas Reinhardt treinha...@wheelingil.gov

Re: I'm embarrassed to be an AHJ(The Chief's thinking is disturbing)

2009-06-17 Thread Jay Jay Blocker
I guess im really confused on this.  Who is the AHJ here?  State or local? From: J. Scott Mitchell jsmfir...@yahoo.com To: sprinklerforum@firesprinkler.org Sent: Wednesday, June 17, 2009 6:44:57 PM Subject: Re: I'm embarrassed to be an AHJ(The Chief's thinking

RE: Slow responding dry pipe valves

2009-06-17 Thread Damien Shannon
George. Sorry for the delay in responding, but I didn't immediately get through to the website www.stinkcad.com. I therefore had to get my IT guy over, who in turn got on to our internet provider. They are looking into it and will contact me when they have a solution. I'm sure it will be worth