OFF FORUM HELP

2010-02-18 Thread Karen Purvis
Is there anyone who would be willing to help me off forum with some design questions and calculation questions? Karen Purvis Senior Designer Facility Systems Consultants 713 South Central Street, Suite 101 Knoxville, TN 37902 ph.865-246-0164 fax 865-246-1084

thanks for offers

2010-02-18 Thread Karen Purvis
Thanks to everyone for the offers of help. I have found my answers this time but may have more later. Karen Purvis Senior Designer Facility Systems Consultants 713 South Central Street, Suite 101 Knoxville, TN 37902 ph.865-246-0164 fax 865-246-1084

RE: Help

2010-02-18 Thread Chris Cahill
True the code might give you guidance. But the more fundamental is who is intended to use the standpipe. Untrained people - Class II, FD only - Class I, either - Class III. And if it's FD the spacing, pressure and size is up to them especially if not in USA. In other words maybe the FD would

Written pump test procedures

2010-02-18 Thread Craig.Prahl
Does anyone have written fire pump test procedures that they'd be willing to share? I need for electric and for diesel. Time is my enemy and I'd rather edit an existing then create from scratch if possible. Thanks Craig L. Prahl, CET Fire Protection Specialist Mechanical Department

RE: Help

2010-02-18 Thread Ing. Levent Numanoglu
Hello all once again and thank you for the valuable time and answers. Ron as you mentioned, yes the prison facility and where my office is in Mexico but I am in the city and the facility is in the middle of nowhere. I will definitely discuss the points which you have outlined about the evacuation

Re: Help

2010-02-18 Thread Ron Greenman
Levent, Seems to me that developing a water supply for a standpipe system in the middle of nowhere will be far more expensive than doing the same for a sprinkler system, including the sprinkler system itself. The tank size and pump size can just be so much smaller in the latter scenario. There is

Under/Over Sprinkler

2010-02-18 Thread James Zimmerman
Has anyone seen/used the term under/over sprinkler on a set plans? Someone in my office has a set of plans where the contractor called out the sprinklers as under/over sprinklers. At first I thought maybe it was describing pendant sprinklers below the ceiling and upright above, protecting a

RE: Under/Over Sprinkler

2010-02-18 Thread George Church
Above and below is the usual slang for what I'd think he means. And maybe the contract dwgs showed above and below, referred to it as under/over, and maybe this is a plumber who doesn't know you don't need uprights in noncombustible spaces, maybe the AE doesn't care, they're on the docs and its

RE: Under/Over Sprinkler

2010-02-18 Thread Craig.Prahl
Depending on the conditions of the project in regards to an underwriter or other AHJ requirement, contents such as piping, wiring, HVAC equipment, ducting, etc. could be combustible and drive an underwriter to require above ceiling protection due to the combustible loading of the contents, not

Re: Under/Over Sprinkler

2010-02-18 Thread James Zimmerman
No equipment shown on the plans except for in the mechanical room. They are showing these sprinklers throughout the building, including the stairwells. Basically everywhere there is a ceiling. On Thu, Feb 18, 2010 at 10:58 AM, craig.pr...@ch2m.com wrote: Depending on the conditions of the

RE: Under/Over Sprinkler

2010-02-18 Thread Todd Williams
Cloud ceiling? At 11:58 AM 2/18/2010, you wrote: Depending on the conditions of the project in regards to an underwriter or other AHJ requirement, contents such as piping, wiring, HVAC equipment, ducting, etc. could be combustible and drive an underwriter to require above ceiling protection

Re: Under/Over Sprinkler

2010-02-18 Thread Forest Wilson
I just read it again. The detail for the upright sprinkler may be an Old Style sprinkler. Forest Wilson Project Manager Cherokee Fire Protection Co. 1855 Bellbrook Ave. Ste C Xenia OH 45385 ph: 937-376-2333 fx: 614-455-4324 cell: 937-307-5647 . Visit our blog: www.cherokee-fire.blogspot.com

Re: Under/Over Sprinkler

2010-02-18 Thread James Zimmerman
No clouds. I hadn't thought about the possible reference to a conventional style sprinkler. I'll have to check back with the review and see if they got a response from the contractor. On Thu, Feb 18, 2010 at 11:04 AM, Matthew J. Willis m...@norredfire.comwrote: Also know as Conventional, and

Re: Under/Over Sprinkler

2010-02-18 Thread jhoffman
NFPA 13 has a pipe schedule for above and below a ceiling (table 22.5.3.7 2007 edition). You mention concrete floors, just be sure there is no combustible form board that remains in place if you are proposing to eliminate the above sprinklers. John Hoffman P.E. | Fire Protection Engineer |

Re: Written pump test procedures

2010-02-18 Thread Craig Leadbetter
Has anyone shared this info yet? I would be interested if someone wants to share. thanks Craig Leadbetter Safeguard of Marquette (O) 906-475-9955 (F) 906-475-5474 (C) 906-362-5393 At 10:30 AM 2/18/2010, you wrote: Does anyone have written fire pump test procedures that they'd be

RE: Under/Over Sprinkler

2010-02-18 Thread George Church
Matt's right, unlikely there's a fur vault intended use above the ceiling, unless critters die. You WILL let us know why they'd have concealed heads below, uprights above, a ceiling in a non-combustible stair tower? light bulb ON IS IT A GOVERNMENT JOB??? That might explain everything. glc

Re: Under/Over Sprinkler

2010-02-18 Thread James Zimmerman
I will definitely let everyone know as soon as we get a response. Thanks for the insights. On Thu, Feb 18, 2010 at 12:18 PM, George Church for...@ptd.net wrote: Matt's right, unlikely there's a fur vault intended use above the ceiling, unless critters die. You WILL let us know why they'd

RE: Written pump test procedures

2010-02-18 Thread Tom Duross
I have a memo of responsibilities (Owner and Contractor) and duties I'd be happy to share with anyone that want it but I do a little more than what's required, somewhere between annual and start-up. Tom Duross Email me off-list if interested. Has anyone shared this info yet? I would be

Spklr in non comb space

2010-02-18 Thread Todd Williams
I am working on a classroom building with cloud ceilings in each of the classrooms. Construction is concrete on steel beams. Sprinklers are to be installed bothabove and below the cloud. The space between the ceiling and the deck is 2'-6. 8.15.1.6 calls for concealed space sprinklers in

RE: Written pump test procedures

2010-02-18 Thread Thomas Reinhardt
Try N.F.P.A. 20 or the Fire Pump Handbook by Puchovsky and Isman.I hope this helps Tom Reinhardt Wheeling Fire Inspector 2 Community Boulevard Wheeling,IL 60090 phone 847-499-9067 -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Spklr in non comb space

2010-02-18 Thread Dan Wilder
I am not sure this qualifies as a combustible concealed space (combustible enclosure being key words) as much as a ceiling mounted obstruction. Your situation leads me more along the lines of the obstruction rules (8.6.5.3-2007). 8.15.1.6 also specifically calls out wood truss/joist/double

RE: Spklr in non comb space

2010-02-18 Thread Brad
I agree- light haz- probly obst. Const. at the deck (if the beams are not too far apart), ignore the clouds 1st, sprinkler the floor spaced to the walls-- then drop pend heads in the clouds spaced to the edge of the clouds -Original Message- From: Dan Wilder [mailto:d...@desertfire.com]

RE: Spklr in non comb space

2010-02-18 Thread A.P.Silva
Correct. Tony -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams Sent: February 18, 2010 2:13 PM To: sprinklerforum@firesprinkler.org Subject: Spklr in non comb space I am working on a classroom

Re: Written pump test procedures

2010-02-18 Thread bverhei
Craig: I'd go with the well considered checklists by Mike Thrapp, of Oregon, sold by ICC . http://www.iccsafe.org/Store/Pages/Product.aspx?category=940cat=ICCSafeid=4408X06 table of contents http://www.iccsafe.org/Store/Documents/TOC/4408s06.pdf excerpt from preface For each