RE: [EXTERNAL] RE: FDC & Pump

2018-01-31 Thread Kyle . Montgomery
I disagree. From NFPA 13, 2016 edition:

8.17.2.4.3 For multiple systems, the fire department connection shall be 
connected between the supply control valve and the system control valves.

Wouldn’t that be on the riser manifold? The handbook even goes on to explain 
why this would be the preferable arrangement.

Am I misinterpreting this?

-Kyle M


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Tom Duross
Sent: Wednesday, January 31, 2018 3:36 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: [EXTERNAL] RE: FDC & Pump

What Larry said..
And there can’t be any valves between the FDC and the FDV’s on the standpipe 
unless you have more than one standpipe and have isolation valves at the base 
of each standpipe so you can’t take them off the riser manifold, for example.
TD


The requirement is from NFPA 13, not from NFPA 20. Here is the text from NFPA 
13-2013:

8.17.2.4.8  Fire department connections shall not be connected on the suction 
side of fire pumps.

Larry Keeping


I have always installed FDC's on the discharge side of fire pumps.  Looking 
through 2013 NFPA 20, I don't see anything precluding the instillation on the 
supply side.  Is the FDC allowed to be installed on the supply?
I have a contractor that has installed the FDC on the supply run-in, instead of 
stubing up a secondary line from the remote FDC.
Thanks,
Jamie
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: FDC & Pump

2018-01-31 Thread Tom Duross
and also allowed, the FDC check….

duh

 

 

What Larry said..

And there can’t be any valves between the FDC and the FDV’s on the standpipe 
unless you have more than one standpipe and have isolation valves at the base 
of each standpipe so you can’t take them off the riser manifold, for example.

TD

 

 

The requirement is from NFPA 13, not from NFPA 20. Here is the text from NFPA 
13-2013:

 

8.17.2.4.8  Fire department connections shall not be connected on the suction 
side of fire pumps.

 

Larry Keeping

 

 

I have always installed FDC's on the discharge side of fire pumps.  Looking 
through 2013 NFPA 20, I don't see anything precluding the instillation on the 
supply side.  Is the FDC allowed to be installed on the supply?

I have a contractor that has installed the FDC on the supply run-in, instead of 
stubing up a secondary line from the remote FDC.

Thanks,

Jamie

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: FDC & Pump

2018-01-31 Thread Tom Duross
What Larry said..

And there can’t be any valves between the FDC and the FDV’s on the standpipe 
unless you have more than one standpipe and have isolation valves at the base 
of each standpipe so you can’t take them off the riser manifold, for example.

TD

 

 

The requirement is from NFPA 13, not from NFPA 20. Here is the text from NFPA 
13-2013:

 

8.17.2.4.8  Fire department connections shall not be connected on the suction 
side of fire pumps.

 

Larry Keeping

 

 

I have always installed FDC's on the discharge side of fire pumps.  Looking 
through 2013 NFPA 20, I don't see anything precluding the instillation on the 
supply side.  Is the FDC allowed to be installed on the supply?

I have a contractor that has installed the FDC on the supply run-in, instead of 
stubing up a secondary line from the remote FDC.

Thanks,

Jamie

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: FDC & Pump

2018-01-31 Thread Jamie Seidl
  
  

 Thanks everyone. I knew why, I just couldn't remember where.   
  

  
  

  
  
>   
> On Jan 31, 2018 at 4:34 PM,  mailto:jnor...@rlhfp.com)>  wrote:
>   
>   
> 
>   
>
> Last time I looked the FDC was not allowed on the suction side.That 
> requirement was in NFPA 13 under the FDC location section.
>
>   
>
>   
>
>   
>
>   
>
>   
>
> Jason Norton, PE – RLH Fire Protection
>
>   
>
> Direct: (661) 410-1334, Mobile: (661) 979-6301, Fax: (661) 322-6816
>
>   
>
> Mailing Address: PO Box 42470, Bakersfield, CA 93384
>
>   
>
>   
>
>   
>
> From:  Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
>  On Behalf Of  Jamie Seidl
>   Sent:  Wednesday, January 31, 2018 1:30 PM
>   To:  sprinklerforum@lists.firesprinkler.org
>   Subject:  FDC  &  Pump
>
>   
>
>   
>
>   
>   
>   
>   
>   
>
> I have always installed FDC's on the discharge side of fire pumps.Looking 
> through 2013 NFPA 20, I don't see anything precluding the instillation   on 
> the supply side.Is the FDC allowed to be installed on the supply?
>
>   
>   
>   
>
> I have a contractor that has installed the FDC on the supply run-in, instead 
> of stubing up a secondary line from the remote FDC.
>
>   
>   
>   
>
> Thanks,
>
>   
>   
>   
>
> Jamie
>
>   
>   
>   
>   
>   
>  ___ Sprinklerforum mailing list 
> Sprinklerforum@lists.firesprinkler.org 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>   
  
  
 ___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: FDC & Pump

2018-01-31 Thread Larry Keeping
The requirement is from NFPA 13, not from NFPA 20. Here is the text from NFPA 
13-2013:

8.17.2.4.8  Fire department connections shall not be connected on the suction 
side of fire pumps.

Larry Keeping

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jamie Seidl
Sent: January-31-18 4:30 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: FDC & Pump

I have always installed FDC's on the discharge side of fire pumps.  Looking 
through 2013 NFPA 20, I don't see anything precluding the instillation on the 
supply side.  Is the FDC allowed to be installed on the supply?
I have a contractor that has installed the FDC on the supply run-in, instead of 
stubing up a secondary line from the remote FDC.
Thanks,
Jamie
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: FDC & Pump

2018-01-31 Thread Prahl, Craig/GVL
The FDC is for pressurizing the loop in the event that the main fire pump is 
out of service and you have to use the pumper apparatus.


Craig L. Prahl
Fire Protection Group Lead/SME
Direct - 864.920.7540
Fax - 864.920.7129
Direct Extension  77540
CH2M is now Jacobs.
200 Verdae Blvd.
Greenville, SC  29607
craig.pr...@ch2m.com
http://www.jacobs.com

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jamie Seidl
Sent: Wednesday, January 31, 2018 4:30 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: FDC & Pump [EXTERNAL]

I have always installed FDC's on the discharge side of fire pumps.  Looking 
through 2013 NFPA 20, I don't see anything precluding the instillation on the 
supply side.  Is the FDC allowed to be installed on the supply?
I have a contractor that has installed the FDC on the supply run-in, instead of 
stubing up a secondary line from the remote FDC.
Thanks,
Jamie
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: FDC & Pump

2018-01-31 Thread Matt Grise
The pump will still boost its inlet pressure. If you use the FDC to boost the 
inlet pressure to 175, then the pump will discharge 175 + pump pressure. Could 
be too much.

Matt

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jamie Seidl
Sent: Wednesday, January 31, 2018 3:30 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: FDC & Pump

I have always installed FDC's on the discharge side of fire pumps.  Looking 
through 2013 NFPA 20, I don't see anything precluding the instillation on the 
supply side.  Is the FDC allowed to be installed on the supply?
I have a contractor that has installed the FDC on the supply run-in, instead of 
stubing up a secondary line from the remote FDC.
Thanks,
Jamie
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: FDC & Pump

2018-01-31 Thread Jason Norton
Last time I looked the FDC was not allowed on the suction side.  That 
requirement was in NFPA 13 under the FDC location section.


Jason Norton, PE – RLH Fire Protection
Direct: (661) 410-1334, Mobile: (661) 979-6301, Fax: (661) 322-6816
Mailing Address: PO Box 42470, Bakersfield, CA 93384

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jamie Seidl
Sent: Wednesday, January 31, 2018 1:30 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: FDC & Pump

I have always installed FDC's on the discharge side of fire pumps.  Looking 
through 2013 NFPA 20, I don't see anything precluding the instillation on the 
supply side.  Is the FDC allowed to be installed on the supply?
I have a contractor that has installed the FDC on the supply run-in, instead of 
stubing up a secondary line from the remote FDC.
Thanks,
Jamie
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


FDC & Pump

2018-01-31 Thread Jamie Seidl
I have always installed FDC's on the discharge side of fire pumps.  Looking
through 2013 NFPA 20, I don't see anything precluding the instillation on
the supply side.  Is the FDC allowed to be installed on the supply?
I have a contractor that has installed the FDC on the supply run-in,
instead of stubing up a secondary line from the remote FDC.
Thanks,
Jamie
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org