and also allowed, the FDC check….

duh

 

 

What Larry said..

And there can’t be any valves between the FDC and the FDV’s on the standpipe 
unless you have more than one standpipe and have isolation valves at the base 
of each standpipe so you can’t take them off the riser manifold, for example.

TD

 

 

The requirement is from NFPA 13, not from NFPA 20. Here is the text from NFPA 
13-2013:

 

8.17.2.4.8  Fire department connections shall not be connected on the suction 
side of fire pumps.

 

Larry Keeping

 

 

I have always installed FDC's on the discharge side of fire pumps.  Looking 
through 2013 NFPA 20, I don't see anything precluding the instillation on the 
supply side.  Is the FDC allowed to be installed on the supply?

I have a contractor that has installed the FDC on the supply run-in, instead of 
stubing up a secondary line from the remote FDC.

Thanks,

Jamie