Re: Gridded dry system

2021-10-27 Thread BRUCE VERHEI via Sprinklerforum
Is the dry system water delivery software capable of modeling this configuration, using a given water supply? Best. Bruce Verhei > On 10/27/2021 9:50 AM Kevin Hall via Sprinklerforum > wrote: > > > If the pipe marked in red is removed and capped off, it eliminates any > split

RE: Gridded dry system

2021-10-27 Thread Ed Kramer via Sprinklerforum
I do love a good can of worms! I fully expected differing opinions on this. Ultimately, it comes down to how much delay there will be getting water to any given open sprinkler and how much delay is deemed acceptable. If system volume is less than 750 gpm (yes, a QOD is required) and it's not

Re: Gridded dry system

2021-10-27 Thread Skyler Bilbo via Sprinklerforum
IMHO, defining a grid as any system that can supply a sprinkler from more than one direction is a poor threshold. Just because you install sprinklers on a looped main or line, does not magically turn it into a gridded system. The location of the sprinklers should have nothing to do with it. May I

RE: Gridded dry system

2021-10-27 Thread Chad Mitchell via Sprinklerforum
Here is an Informal Interpretation of a similar layout from November 13, 2009. https://www.dropbox.com/sh/8e4v0xvfri07c5i/AADbhtdz25iS_1Qkdbnh1lWqa?dl=0 Regards, Chad Mitchell Mid Atlantic Fire Protection, Inc. -Original Message- From: Sprinklerforum On Behalf Of J H via

Re: Gridded dry system

2021-10-27 Thread J H via Sprinklerforum
So, on any looped system, if you add sprinklers to the looped main (adding flow from more than two directions) does that now constitute a grid? I see both viewpoints but am posing as devil's advocate. As I said I would steer clear from the original scenario unless necessity dictated otherwise. JH

Re: Gridded dry system

2021-10-27 Thread J H via Sprinklerforum
I would call it a Tree/Loop hybrid. :-P The branchlines are not connecting two parallel cross mains per the definition of a grid. JH On Wed, Oct 27, 2021 at 9:50 AM Kevin Hall wrote: > If the pipe marked in red is removed and capped off, it eliminates any > split flows/transfer lines on the

Re: Gridded dry system

2021-10-27 Thread Kevin Hall via Sprinklerforum
If the pipe marked in red is removed and capped off, it eliminates any split flows/transfer lines on the branch lines. So with the red pipe removed I would define it as a tree. With the red pipe installed, I would define it as a grid. The above is my opinion and has not been processed as a formal

Re: Gridded dry system

2021-10-27 Thread J H via Sprinklerforum
So, for discussions sake take a look at the image link - what would you all call this system? I have my opinion but I don't see how it's much different than Ed's original drawing: https://ibb.co/xSW04dj On Wed, Oct 27, 2021 at 9:46 AM J H wrote: > So, for discussions sake take a look at the

Re: Gridded dry system

2021-10-27 Thread Kevin Hall via Sprinklerforum
Yes, I see that now... looks like I have another PI to add to the NFPA 13 list. Look for that line of sprinklers to be removed in the 2025 edition haha. The above is my opinion and has not been processed as a formal interpretation in accordance with the NFPA Regulations Governing Committee

Re: Gridded dry system

2021-10-27 Thread J H via Sprinklerforum
Kevin, That's true for most of the sprinklers in the diagram but look at figure A.3.3.206.6 (2019) - the farthest loop from the supply has sprinklers on it and it's connecting both loops - those sprinklers are receiving water from two mains. Likewise, per the definition of a main the only main in

Re: Gridded dry system

2021-10-27 Thread Kevin Hall via Sprinklerforum
The annex shows the branch lines fed by the cross main from two directions, the sprinkler can still only receive water from one direction from the branch line... that is the distinction in the definition. The above is my opinion and has not been processed as a formal interpretation in accordance

Re: Gridded dry system

2021-10-27 Thread J H via Sprinklerforum
I have a problem with the simplified definition floated out here that a grid system is one that feeds a sprinkler from two directions because of the illustration of a looped system in the annex of '13 which shows sprinklers attached to the end portion of the loop resulting in those sprinklers

RE: Gridded dry system

2021-10-27 Thread Sean Conlin via Sprinklerforum
If you were to put caps on the left and right lines going north and south, it resembles a compound gridded system and a sprinkler can receive water from both sides. The east and west lines are essentially the mains and so is the 4" in the middle. Yes is has a looped piping arrangement and

RE: Attic Piping

2021-10-27 Thread Brian Harris via Sprinklerforum
Thanks Mickey! Brian Harris, CET BVS Systems Inc. bvssytemsinc.com -Original Message- From: Sprinklerforum On Behalf Of Mickey Ferguson via Sprinklerforum Sent: Wednesday, October 27, 2021 7:57 AM To: Mickey Ferguson ; sprinklerforum@lists.firesprinkler.org Cc: Mickey Ferguson ; Brian

RE: Attic Piping

2021-10-27 Thread Brian Harris via Sprinklerforum
Thanks Mike! Brian Harris, CET BVS Systems Inc. bvssytemsinc.com -Original Message- From: Sprinklerforum On Behalf Of Mike Morey via Sprinklerforum Sent: Wednesday, October 27, 2021 7:55 AM To: sprinklerforum@lists.firesprinkler.org Cc: Mike Morey Subject: RE: Attic Piping We don't

RE: Attic Piping

2021-10-27 Thread Brian Harris via Sprinklerforum
Taylor- Thank you. Brian Harris, CET BVS Systems Inc. bvssytemsinc.com -Original Message- From: Sprinklerforum On Behalf Of Taylor Schumacher via Sprinklerforum Sent: Wednesday, October 27, 2021 7:53 AM To: sprinklerforum@lists.firesprinkler.org Cc: Taylor Schumacher Subject: RE:

RE: Attic Piping

2021-10-27 Thread Mickey Ferguson via Sprinklerforum
For the safety of the installers so they do not have to climb up in the top of an attic or have to make make-shift ladders, I typically try to put the main down the middle for the BB's at chest high and use sprigs. This also helps with getting over mechanical equipment/duct that may be in the

RE: Attic Piping

2021-10-27 Thread Brian Harris via Sprinklerforum
Todd- Thank you. Brian Harris, CET BVS Systems Inc. bvssytemsinc.com -Original Message- From: Sprinklerforum On Behalf Of Fpdcdesign via Sprinklerforum Sent: Wednesday, October 27, 2021 7:24 AM To: Sprinklerforum Cc: Fpdcdesign Subject: Re: Attic Piping I typically use

RE: Attic Piping

2021-10-27 Thread Mike Morey via Sprinklerforum
We don't do many, but over the years I've done a decent amount personally, some of my experience is dated and/or lacks trial and error honing but my 2 cents worth is: I always use BBs when I can, make sure you look at each of the 3(at least) offerings of them currently as they have different

RE: Attic Piping

2021-10-27 Thread Taylor Schumacher via Sprinklerforum
Good morning Brian, Your fitters will hate you if they have to set the main high towards the ridge. The best way is to use a single main, hung low, with 1" or 1-1/4" sprigs to the back to back sprinklers at the ridge. If you have a mechanical chase that extends in to the attic, you may have to

Re: Attic Piping

2021-10-27 Thread Fpdcdesign via Sprinklerforum
I typically use option 2. Sometimes the framing at the peak can be a little funky and it is easier to adjust a smaller line. Also, I will put 1” outlets on any welded pipe for attic sprinklers, in case sprigs become necessary. Todd G Williams, PE Fire Protection

Attic Piping

2021-10-27 Thread Brian Harris via Sprinklerforum
Seems were seeing more and more wood framed buildings these days and with that comes attics. Just curious what the general school of thought is with running piping in these spaces. Is it better to run the Main high under the ridges with back to back heads (size permitting) or is it better run