Why would they have used antifreeze in a dwelling. The only time I design
with that mixture is when the system is outside. Am I missing something.
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
Is there anyone who would be willing to help me off forum with some design
questions and calculation questions?
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
Thanks to everyone for the offers of help. I have found my answers this time
but may have more later.
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
worked
for me but now I have someone questioning my method. Should I be going back
to the pipe schedule method?
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
We mainly do new and add-on systems a few retrofits no grids no high piled
storage no extra hazard. Usually all light and ordinary hazard.
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
I'm not talking about calculations just about selecting the actual size of
the pipe. Should I use a 1 pipe on 2 sprinklers or use a 1 pipe as long as
the gpms are less than 10. I just want to know how people know or choose the
size of pipe they use for each branch, sprig and main.
Karen Purvis
Can anyone give me a definition of indicating shut-off valve. My guess is
that it is an OS Y but don't know.
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
Yes this answered the question, which of course was the answer I thought but
was prompted to ask anyway. Thanks all.
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
-Original Message-
From
Where in the code does it say that you cannot mix systems in an area. In
other words if I have a large room that a section of the room is separated
by a chain link fence and one side has a wet system and the other side needs
a preaction system. Where does it tell me I can't do that?
Karen
The reason for the different system is that behind the fence is a switch
gear (electric) and the owner does not want the chance that it will get wet.
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
It is smoke detection activated and the other area is basically a hallway.
The other questions I can't answer. I will look into these things but I
mainly need to know can you mix systems in an area?
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Yes I think you understand the area and it is an egress hallway. All of this
is in the lower level or mechanical area of an airport.
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
-Original
As for rest of hallway yes across its 4 or 5 feet but it's part of a maze of
open hallways so where would you end the PA system. The question could go on
and on. Thank you for all the help this forum rocks!
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite
me or reading that in a 13R or 13D system if the areas mentioned were net
being used or accessed then they did not need to be sprinkled. Is this
something I dreamed up?
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865
Yes it is 13D and I did finally find the reference. Thanks
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
I went back and looked again an I was correct the first time, this will be
done as a 13D system.
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
-Original Message-
From: sprinklerforum-boun
No lets just say that Karen is doing 5 things at once and trying to get
three jobs out and can't seem to keep them separate and keep confusing jobs.
Doh.13R is the correct answer. Can the holiday get here any faster?
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central
I have one I could fax you.
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org
Can anyone tell me, does NFPA 13 or 14 say anything about a particular
safety factor to be used in the hydraulic calculations?
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
there is something other than residential in the building
would I not need a backflow on the riser?
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
I use the double check because there IS commercial or just
use a single check BECAUSE its 13R.
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
-Original Message-
From: sprinklerforum-boun
You are right about the double check I have up to now always put one on a 13
or 13R system but while looking for something else I came across the 6.7.1.6
reference and it made it sound like for a 13R system you did not need it.
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South
into a ordinary hazard area.
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
___
Sprinklerforum mailing list
http://lists.firesprinkler.org
what there called) do I need to do something special there (other than
covering above and below them)?
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
I have done a few of these type systems. Usually the ones I have done
involve a mechanical room with a gas furnace or an elevator equipment room.
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
Could someone who deals with Tennessee state FM contact me off forum at :
kpur...@facilitysystems.org.
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
of
building. They claim that I can have the risers in the same room but that
each building section must have a separate riser.
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
The buildings are actually just additions to an existing building and they
are separated by two adjacent fire walls.
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
-Original Message-
From
I know that at one point I found a reference to heat tracing being allowed
under certain conditions. Now I can't find it any help.
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
THANK YOU
Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf
I have done several prisons and have always counted any evidence room
(either paper or object storage) as OHII. The fire Marshalls here have never
sent it back to be changed.
Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
to
sprinkle the entire attic, and would it need to be dry, or should I have
them enclose the walkway and just sprinkle the mech room?
Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
the
design has three extended coverage heads below the opening. They wanted us
to put heads up at the apex of the window but through an exception now want
us to put smoke detectors at the top and 10 (ten) heads around the sides.
Does this sound unreasonable to anyone else?
Karen Purvis
Designer
Facility
The only code cited was 8.6.4.1.3 but this is concerning pendent heads and
we were designing using sidewalls and throwing across the area.
Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
-Original Message-
From: [EMAIL
According to NFPA 13 10.10.2.5.1 I have to have a backflow prevention
assembly but does not tell what that is or what it is to include. Can anyone
give me that info?
Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
of
flowing the design water demand for the system.
I showed a detail that included a zurn backflow going to an alarm check and
on up to the FDC then to the riser.
Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
Thanks to all for the help on the pit detail.
Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http
I am in need of a typical city water pit detail showing valve
arrangements if anyone could share one with me it will save me some
time.
Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
That's ok I'm not running on all cylinder either your right about the 21'.
The response before this by Art answered my confusion. I thought the 30'
included any outlet that might or might not have to be placed on the roof.
Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville
is
steel framed enclosure panels with panel inserts. Enclosure gates are also
steel. My guess is that I would treat this as like a vertical shaft and have
one head at the top and then cover the equipment room like I would an
elevator equipment room but I am open for comments.
Karen Purvis
Designer
I have a question for anyone working today. There is a code somewhere that
states when a standpipe must be used. I have searched through NFPA 14 and 13
and can not find the code. Does anyone know what and where that information
is?
Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Thank you everyone. It helps if you look in the correct code book :).
Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
___
Sprinklerforum mailing list
Sprinklerforum
. The only
code I see that possibly address this is 21.20.1.2.1 and it only says you
have to use automatic heads. Any help!
Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
Thank you to all who responded. My problem however is that the area that I
am covering is not an atrium. It is a ramp that goes up three stories with
exits at each floor. Since this is not labeled as an atrium do all the
comments I have received still hold true?
Karen Purvis
Designer
Facility
I don't know if anyone is interested but if you are on Myspace there is
now a sprinkler group: http://groups.myspace.com/firesprinkler
Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
but the third
one needs to go over an exposed area can it connect on the third floor to
the closest pipe or is there a better way of connecting them.
Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
pressure is such that I will have to have a pump no matter what I do because
the pressure is low to begin with.
Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL
?
Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
I would love to see a copy of yours and anyone else's spreadsheets for
calcs. I am always trying to improve on what I have.
Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
-Original Message-
From: [EMAIL PROTECTED
calcs by hand and so I created Excel spreadsheets to help.
Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris
Sent: Wednesday, July
be very high. Any thoughts on this.
Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http
But the question still is; is there somewhere in the code that states that
this is how you treat a steamroom. In other words do I have to have that
area covered?
Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
-Original
I could not find anything either but the engineer did not think it would
need to be covered. Just trying to cover my bases.
Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
-Original Message-
From: [EMAIL PROTECTED
Question: Is/was there a 2003 edition of the NFPA 13? I have 2002 and
2007
Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
___
Sprinklerforum mailing list
Sprinklerforum
That was what I thought but I got a markup saying it was 2003. Thanks.
Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Cliff
Whitfield
know
these courts have been around for years so at some point someone has
sprinkled them Any help would be great.
Karen Purvis
Designer
Facility Systems Consultants
Knoxville, TN 37902
865-246-0164
___
Sprinklerforum mailing list
Sprinklerforum
No if you have ever played or watched anyone play you use the entire court.
That includes floor ceiling and walls. The ball hits all over. Piping inside
would obstruct play and a upright head would get hit a lot.
Karen Purvis
Designer
Facility Systems Consultants
Knoxville, TN 37902
865-246-0164
I have a situation where the building has a 1'9 wood floor joist
construction and I am being asked if it needs to be sprinkled. If so what
type and how many heads. I say that by 8.14.1.2.1 that it does not or may
not need to be sprinkled but I just don't know. Any help would be great.
Karen
After looking back at my notes this system is a 13 system. The members are
2' deep wood web joist. So my guess is that we would treat it as a light
hazard and use upright heads. Does this sound right? Then my next question
is do I have to account for the web member obstructions?
Karen Purvis
This is not in the ceiling. This is the joist between two floors.
Karen Purvis
Designer
Facility Systems Consultants
Knoxville, TN 37902
865-246-0164
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
Sent: Friday, December 22, 2006 11:39 AM