RE: PODs storage again

2009-03-31 Thread Ray Vance
Travis,

This product commodity falls within the same parameters as boat storage - there 
is no prescriptive requirement to follow.
In fact, NFPA has issued a statement this particular type of storage 
arrangement is outside the scope of NFPA-13.

That being said, I have done a fair amount of research into the PODS type 
storage arrangements for my own education and can offer the following as a 
starting point (guidelines) for your consideration.

(A) I spoke, at length, with Ms. Elley Klausbruckner at Klausbruckner and 
Assoc. regarding the general requirements for this PODS type storage and 
specifically about your particular type of storage arrangement. Ms. 
Klausbruckner is a fire protection engineer and specializes in HPR risk 
analysis and protection and has been involved in many warehouse storage 
arrangements of this PODS/Crate type storage, including the brand name PODS 
facilities.
(B) In all cases except one, they have designed the fire sprinkler system as an 
Exposed, Unnexpanded, Group-A plastic commodity storage arrangement.
(C) In all cases except one, they have designed utilizing ESFR sprinklers, 
unless the building construction prohibited the ESFR protection. In the 
scenario where the building construction would not allow ESFR, they designed 
utilizing the area/density method for the appropriate storage height.
(D) In the one case where they did NOT protect as a Group-A plastic commodity 
the pods/crates were constructed entirely of wood. In this scenario they 
required a letter from the owner of the facility that the amount of Group-A 
plastics within the pods/crates at any time were less than 5% to 15% by weight 
or 5% to 25% by volume. The crate itself was treated as part of the unit load 
and the entire unit load was classified as a Class-IV commodity.
(E) For reference, upholstered furniture is classified as a Class-IV commodity 
per the IFC 2303.5 (See IFC Figure 2303.7.4)
(F) Tyco Fire Products, per their own internal technical document also 
indicates ESFR protection for PODS type storage that have plastic tops on the 
containers.
(G) An analysis done by Rolf Jensen and Associates and written up in the 2006 
Edition of Fire Protection Engineering Magazine suggests the use of ESFR 
sprinklers for the Group-A plastics scenario as well, but also indicates a dual 
design area/density as another design option.

I know some of our esteemed colleagues are still not entirely comfortable with 
the determination of the protection schemes for this particular type of storage 
and there is NO prescriptive direction from NFPA on the subject. However, they 
have been and are being built all over the country and are being sprinklered in 
some fashion. We can only provide the protection scheme that is most consistant 
with the experts in our field, FP engineers with risk analysis experience, 
and provide the protection scheme as determined by them.

The consensus from my personal research, at least at this point, is to protect 
as an Exposed, Unexpanded, Group-A plastic commodity and provide ESFR 
protection if the building construction allows.

I implore those of you with the expertise above and beyond what Travis and I 
have to weigh in and provide your insights and experiences into this commodity 
storage.

As always, have and AWESOME day!

Ray Vance - SET
Wayne Automatic Fire Sprinklers, Inc.
www.waynefire.com
(407) 877-5563   office
(321) 436-2184   mobile

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Travis Mack, SET
Sent: 2009-03-30 5:30 PM
To: sprinklerforum@firesprinkler.org
Subject: PODs storage again

I tried to search the archives, but keep getting a file not found error.  I am 
looking at a PODs storage warehouse.  There was a lot of discussion on the 
forums a while back, but I can't access all of it.  The facility I am looking 
at has 24' storage.

What is the general concensus of the protection req'd for these areas?

Thanks in advance for your help.



Travis Mack, SET
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: PODs storage again

2009-03-31 Thread Chris Cahill
The only hole in the thinking of the experts is their opinions are based
on WAG not SWAG to my knowledge.  I'm not suggesting they are wrong. I'd
trust their knowledge a bit more if they had some test data (which doesn't
exist) or at least some examples of fires and the outcome.  Sure would be
nice if they point to a fire with ESFR that was successfully contained.  Has
that happened and I'm not aware definitely probable. 

Think of it like this you see a problem with system and the contractor says
well I've always done it like that.  Doesn't make it right does it?  

And ESFR scares me a bit with its tendency to either work fully or burn the
place down.  At least with density systems there is a little reserve in my
experience. 

And I'm totally comfortable if Elley or Rolf sign the design as EOR.  Make
it LH and I'm cool with their design.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: chr...@sentryfiremn.com
 
Mail: P.O. Box 69
Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
  Waverly, MN 55390

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ray Vance
Sent: Tuesday, March 31, 2009 8:09 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: PODs storage again

Travis,

This product commodity falls within the same parameters as boat storage -
there is no prescriptive requirement to follow.
In fact, NFPA has issued a statement this particular type of storage
arrangement is outside the scope of NFPA-13.

That being said, I have done a fair amount of research into the PODS type
storage arrangements for my own education and can offer the following as a
starting point (guidelines) for your consideration.

(A) I spoke, at length, with Ms. Elley Klausbruckner at Klausbruckner and
Assoc. regarding the general requirements for this PODS type storage and
specifically about your particular type of storage arrangement. Ms.
Klausbruckner is a fire protection engineer and specializes in HPR risk
analysis and protection and has been involved in many warehouse storage
arrangements of this PODS/Crate type storage, including the brand name PODS
facilities.
(B) In all cases except one, they have designed the fire sprinkler system as
an Exposed, Unnexpanded, Group-A plastic commodity storage arrangement.
(C) In all cases except one, they have designed utilizing ESFR sprinklers,
unless the building construction prohibited the ESFR protection. In the
scenario where the building construction would not allow ESFR, they designed
utilizing the area/density method for the appropriate storage height.
(D) In the one case where they did NOT protect as a Group-A plastic
commodity the pods/crates were constructed entirely of wood. In this
scenario they required a letter from the owner of the facility that the
amount of Group-A plastics within the pods/crates at any time were less than
5% to 15% by weight or 5% to 25% by volume. The crate itself was treated as
part of the unit load and the entire unit load was classified as a Class-IV
commodity.
(E) For reference, upholstered furniture is classified as a Class-IV
commodity per the IFC 2303.5 (See IFC Figure 2303.7.4)
(F) Tyco Fire Products, per their own internal technical document also
indicates ESFR protection for PODS type storage that have plastic tops on
the containers.
(G) An analysis done by Rolf Jensen and Associates and written up in the
2006 Edition of Fire Protection Engineering Magazine suggests the use of
ESFR sprinklers for the Group-A plastics scenario as well, but also
indicates a dual design area/density as another design option.

I know some of our esteemed colleagues are still not entirely comfortable
with the determination of the protection schemes for this particular type of
storage and there is NO prescriptive direction from NFPA on the subject.
However, they have been and are being built all over the country and are
being sprinklered in some fashion. We can only provide the protection scheme
that is most consistant with the experts in our field, FP engineers with
risk analysis experience, and provide the protection scheme as determined by
them.

The consensus from my personal research, at least at this point, is to
protect as an Exposed, Unexpanded, Group-A plastic commodity and provide
ESFR protection if the building construction allows.

I implore those of you with the expertise above and beyond what Travis and I
have to weigh in and provide your insights and experiences into this
commodity storage.

As always, have and AWESOME day!

Ray Vance - SET
Wayne Automatic Fire Sprinklers, Inc.
www.waynefire.com
(407) 877-5563   office
(321) 436-2184   mobile

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Travis Mack,
SET
Sent: 2009-03-30 5:30 PM
To: sprinklerforum@firesprinkler.org
Subject: PODs storage again

RE: PODs storage again

2009-03-31 Thread Chris Cahill
While true initially the HPR then is replaced next year by Billy Bob Joe's
Insurance and they sue the contractor when it fails.  HPR didn't legally
engineer it as they are not the EOR usually even though they often drive a
design, Codes don't cover it.  You are out on your own at that point.
proceed very cautiously is very wise.   

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: chr...@sentryfiremn.com
 
Mail: P.O. Box 69
Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
  Waverly, MN 55390
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Roland
Huggins
Sent: Tuesday, March 31, 2009 10:59 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: PODs storage again

  If the HPR insurance company makes a judgement call on how to  
protect it and it doesn't work, they pay for the loss.  IF this  
guidance is not in the published HPR Loss Prevention Data sheets, then  
the consult is making the judgement call.  Guess who will likely pay  
for the loss?  Now here's the scary part. If the contractor takes the  
responsibility and provides the judgement  call (typically considered  
consulting/engineering since guidance is not in 13 or other national  
standards) who will likely pay the claim?

The moral of the story is when NFPA 13 does not address it, proceed  
very cautiously.

Roland

On Mar 31, 2009, at 6:50 AM, Chris Cahill wrote:

 The only hole in the thinking of the experts is their opinions are  
 based
 on WAG not SWAG to my knowledge.  I'm not suggesting they are wrong.  
 I'd
 trust their knowledge a bit more if they had some test data (which  
 doesn't
 exist) or at least some examples of fires and the outcome.  Sure  
 would be
 nice if they point to a fire with ESFR that was successfully  
 contained.  Has
 that happened and I'm not aware definitely probable.

 Think of it like this you see a problem with system and the  
 contractor says
 well I've always done it like that.  Doesn't make it right does it?

 And ESFR scares me a bit with its tendency to either work fully or  
 burn the
 place down.  At least with density systems there is a little reserve  
 in my
 experience.

 And I'm totally comfortable if Elley or Rolf sign the design as  
 EOR.  Make
 it LH and I'm cool with their design.

 Chris Cahill, P.E.
 Fire Protection Engineer
 Sentry Fire Protection, Inc.

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: PODs storage again

2009-03-31 Thread Thom McMahon
1. If you can get the insurer to spec the design, good.
2. If the EOR spec's the design, protect yourself as best you can. Refer all
questions of changes to them so they assume responsibility for every
decision.
3. If you as a contractor are asked to make the design decisions, Walk, Run,
take a plane to your favorite get away, but refuse the job.

Sometimes the best thing for both you and the customer is to not do the job,
as presented.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Roland
Huggins
Sent: Tuesday, March 31, 2009 9:59 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: PODs storage again

  If the HPR insurance company makes a judgement call on how to protect it
and it doesn't work, they pay for the loss.  IF this guidance is not in the
published HPR Loss Prevention Data sheets, then the consult is making the
judgement call.  Guess who will likely pay for the loss?  Now here's the
scary part. If the contractor takes the responsibility and provides the
judgement  call (typically considered consulting/engineering since guidance
is not in 13 or other national
standards) who will likely pay the claim?

The moral of the story is when NFPA 13 does not address it, proceed very
cautiously.

Roland


___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


PODs storage again

2009-03-30 Thread Travis Mack, SET
I tried to search the archives, but keep getting a file not found error.  I
am looking at a PODs storage warehouse.  There was a lot of discussion on
the forums a while back, but I can't access all of it.  The facility I am
looking at has 24' storage.  
 
What is the general concensus of the protection req'd for these areas?
 
Thanks in advance for your help.
 
 
 
Travis Mack, SET
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: PODs storage again

2009-03-30 Thread Fletcher, Ron
I think the consensus was to hang the building for from a fusible link
over a pond.

Is it a new building? If so it would be interesting to see what the EOR
or architect did for a hazard analysis.

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Travis
Mack, SET
Sent: Monday, March 30, 2009 2:30 PM
To: sprinklerforum@firesprinkler.org
Subject: PODs storage again

I tried to search the archives, but keep getting a file not found error.
I
am looking at a PODs storage warehouse.  There was a lot of discussion
on
the forums a while back, but I can't access all of it.  The facility I
am
looking at has 24' storage.  
 
What is the general concensus of the protection req'd for these areas?
 
Thanks in advance for your help.
 
 
 
Travis Mack, SET
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: PODs storage again

2009-03-30 Thread Jeff Hewitt
Ron, 

it's better not to use hangers on this one, put it under water.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301

636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fletcher, Ron
Sent: Monday, March 30, 2009 4:37 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: PODs storage again

I think the consensus was to hang the building for from a fusible link
over a pond.

Is it a new building? If so it would be interesting to see what the EOR
or architect did for a hazard analysis.

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Travis
Mack, SET
Sent: Monday, March 30, 2009 2:30 PM
To: sprinklerforum@firesprinkler.org
Subject: PODs storage again

I tried to search the archives, but keep getting a file not found error.
I
am looking at a PODs storage warehouse.  There was a lot of discussion
on
the forums a while back, but I can't access all of it.  The facility I
am
looking at has 24' storage.  
 
What is the general concensus of the protection req'd for these areas?
 
Thanks in advance for your help.
 
 
 
Travis Mack, SET
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)