PROTECTED] On Behalf Of Steve Leyton
Sent: Tuesday, September 30, 2008 10:00 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Window Sprinklers
??? Actually, the only ways that I'm aware of are to use rated glass -
VERY expensive - or window sprinklers. If you don't protect them,
there's
- 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com
-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Chris Cahill
Sent: Tuesday, September 30, 2008 10:46 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Window Sprinklers
Well if it's not mandatory could
Can glass door be protected by a window sprinkler?
Ron Fletcher
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve
Leyton
Sent: Tuesday, September 30, 2008 8:00 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Window Sprinklers
??? Actually
PROTECTED]
http://www.ch2m.com
-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of John O'Connor
Sent: Tuesday, September 30, 2008 11:22 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Window Sprinklers
Food for thought concerning the WS sprinkler application
Well all that's being said gives me cause to drop this hot potato in the
hands of the architect AND engineer and be sure I have a written directive
on how to proceed. I was thinking that I could fall back on the old days and
do what was done thousands of times in the past, but I guess not.
Thanks
Leyton
Sent: Tuesday, September 30, 2008 9:38 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Window Sprinklers
The Tyco tests very conspicuously did not, nor does the listing include
doors or moving casement windows. Fixed glass only, no horizontal
mullions or bumps. The obvious being
AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Window Sprinklers
Well all that's being said gives me cause to drop this hot potato in the
hands of the architect AND engineer and be sure I have a written directive
on how to proceed. I was thinking that I could fall back on the old days and
do
-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Chris Cahill
Sent: Wednesday, 1 October 2008 12:39 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Window Sprinklers
Yep, that's what I'm saying. Of course there are other ways to skin this
cat. Fire rated glass
, September 30, 2008 11:07 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Window Sprinklers
Now the Window sprinkler is an alternate to 2Hr. rating, but in the
situation described, it would appear the school is a fully sprinklered
structure, so under the building code they may have reduced
: Tuesday, September 30, 2008 7:54 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Window Sprinklers
A HA!!! That's the point, isn't it? That the architect failed to
completely design the building and account for the protection of
windows
and likely, the limitations of the window sprinklers
IT has been reported to me (equates to I have not checked the cut
sheet) that the WS sprinklers can not be used on load bearing walls.
Has anyone encountered this aspect?
Roland
On Sep 30, 2008, at 8:37 AM, Steve Leyton wrote:
The Tyco tests very conspicuously did not, nor does the
] On Behalf Of Roland Huggins
Sent: Tuesday, September 30, 2008 2:24 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Window Sprinklers
IT has been reported to me (equates to I have not checked the cut
sheet) that the WS sprinklers can not be used on load bearing walls.
Has anyone encountered this aspect
Steamboat Springs, CO 80488
Tel: 970-879-7952
Fax: 970-879-7926
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill Minkel
Sent: Tuesday, September 30, 2008 11:29 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Window Sprinklers
Educate me here
John,
Go to the Tyco Web Site and look up the data sheet for the head. Give
all the relevant data you are looking for.
http://tyco-fireproducts.com/index.php?P=showE=B=CP=1id=TFP620_07_20
05BK=SearchBL=SB=
Rochester Fire Department
Vance Swisher
Fire
John,
Refer to the Tyco web site. There is considerable information there.
Here is a link to the particular cut sheet on the WS head.
http://www.tyco-fire.com/TD_TFP/TFP/TFP620_07_2005.pdf
G. Tim Stone
G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire