As I recall a big part of the reason that the "Window" sprinkler was so
special was that the rated wall test requires the impact of the fire hose
water on the structure after the fire has burned some specific amount of
time. 100 Psi cold water hitting glazing that is even hot in only a few
spots will shatter. The window sprinkler was able to wet the entire window
surface evenly and dissipate the heat, so when the cold hose water hit it,
nothing happened.

Now the "Window sprinkler" is an alternate to 2Hr. rating, but in the
situation described, it would appear the school is a fully sprinklered
structure, so under the building code they may have reduced the ratings down
to 1 hour. Unfortunately that really doesn't help here, as there is no
approved alternative sprinkler application that is equal to 1 hour rating
either. The cost of testing and such to get a = to 1 Hr. is prohibitive.
Maybe TYCO can do "Window Sprinkler Lite" for 1 hr rated wall assemblies?

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton
Sent: Tuesday, September 30, 2008 9:38 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Window Sprinklers

The Tyco tests very conspicuously did not, nor does the listing include
doors or moving casement windows.   Fixed glass only, no horizontal
mullions or bumps.   The obvious being that the intent is to cool the
glass and maintain separation, not water an opening in hopes of keeping fire
and combustion byproduct from breaching it.

Steve Leyton
Protection Design & Consulting
San Diego, CA

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to