Re: Antifreeze systems

2015-06-05 Thread Jay Stough
That is what we are doing. The AHJ told the GC that antifreeze is much cheaper. I basically told them if they want antifreeze, give the contract to someone else, I won't put it in a residential use. *Jay Stough* NICET IV LAYOUT NICET III ITM On Thu, Jun 4, 2015 at 2:51 PM, Curtis Tower

RE: Antifreeze systems

2015-06-04 Thread Mark A. Sornsin, P.E.
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John Denhardt Sent: Thursday, June 04, 2015 9:12 AM To: 'sprinklerforum@lists.firesprinkler.org' Subject: RE: Antifreeze systems Legally you might get by. But when the lawyers get done with you knew (or should have) as an industry

RE: Antifreeze systems

2015-06-04 Thread Matt Grise
-boun...@lists.firesprinkler.org] On Behalf Of Mark A. Sornsin, P.E. Sent: Thursday, June 04, 2015 12:50 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Antifreeze systems I think the legal case would depend on the harm or potential harm done to humans. If you were litigating

RE: Antifreeze systems

2015-06-04 Thread Dewayne Martinez
Wellen Sent: Thursday, June 04, 2015 7:42 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Antifreeze systems I'm hearing jurisdictions saying that the antifreeze ban does not apply to them. It is my understanding that NFPA intended for the new requirements to apply regardless of what

RE: Antifreeze systems

2015-06-04 Thread John Denhardt
position. -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Dewayne Martinez Sent: Thursday, June 04, 2015 9:57 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Antifreeze systems I agree with Chris on this one. How can

RE: Antifreeze systems

2015-06-04 Thread Curtis Tower
Jay, Was protecting the attic with a dry pipe system not an option??? Curtis Tower Central Fire Protection -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of sprinklerforum-requ...@lists.firesprinkler.org Sent: Thursday, June 04,

Re: Antifreeze systems

2015-06-04 Thread Tom Wellen
I’m hearing jurisdictions saying that the antifreeze ban does not apply to them. It is my understanding that NFPA intended for the new requirements to apply regardless of what standard is in effect. DO NOT INSTALL NEW ANTIFREEZE SYSTEMS AT THIS TIME. Wait for the listed solution

RE: Antifreeze systems

2015-06-04 Thread Matt Grise
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Tom Wellen Sent: Thursday, June 04, 2015 7:42 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Antifreeze systems I'm hearing jurisdictions saying that the antifreeze ban does not apply to them. It is my understanding that NFPA

RE: Antifreeze systems

2015-06-03 Thread Cahill, Christopher
on FORTUNE's 2014 List of 100 Best Companies to Work For -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Travis Mack, SET Sent: Wednesday, June 03, 2015 6:42 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Antifreeze systems

Re: Antifreeze systems

2015-06-03 Thread Travis Mack, SET
Message- From: rongreenman . rongreen...@gmail.com To: sprinklerforum sprinklerforum@lists.firesprinkler.org Sent: Wed, Jun 3, 2015 2:27 pm Subject: Re: Antifreeze systems The reason I have no hair is local jurisdictions thinking they have a better insight into these problems than the committee

Re: Antifreeze systems

2015-06-03 Thread Forest Wilson
@lists.firesprinkler.org Sent: Wed, Jun 3, 2015 2:27 pm Subject: Re: Antifreeze systems The reason I have no hair is local jurisdictions thinking they have a better insight into these problems than the committee because they have a special problem. I think they want the attic system because they're afraid

Re: Antifreeze systems

2015-06-03 Thread rongreenman .
appropriate by the fire marshal. I was under the impression that after September of 2012 you could not install new antifreeze systems without listed solution, which at the present time is not available. He is telling me that it just has to be premixed. When I go to the NFPA website, at http

Re: Antifreeze systems RETORT

2015-06-03 Thread ACCENTFIRE
you could not install new antifreeze systems without listed solution, which at the present time is not available. He is telling me that it just has to be premixed. When I go to the NFPA website, at http://www.nfpa.org/safety-information/for-consumers/fire-and-safety-equipme nt/home-fire

Re: Antifreeze systems

2015-06-03 Thread Travis Mack, SET
was under the impression that after September of 2012 you could not install new antifreeze systems without listed solution, which at the present time is not available. He is telling me that it just has to be premixed. When I go to the NFPA website, at http://www.nfpa.org/safety-information

Antifreeze systems

2015-06-03 Thread Jay Stough
I have an AHJ that is telling me to install an antifreeze system in a 13R attic. They have an ordinance requiring attics to be protected in 13R and 13D systems if deemed appropriate by the fire marshal. I was under the impression that after September of 2012 you could not install new antifreeze

Re: Antifreeze systems

2015-06-03 Thread Parsley Consulting
appropriate by the fire marshal. I was under the impression that after September of 2012 you could not install new antifreeze systems without listed solution, which at the present time is not available. He is telling me that it just has to be premixed. When I go to the NFPA website, at http

Residential Antifreeze systems

2015-03-30 Thread Douglas Hicks
piping, and antifreeze. All the antifreeze systems have expansion tanks, most with about a 2.5 gallon non-UL listed tanks and only 4 have UL listed tanks. At least 2 of the units have leaks at present. One with a UL listed Amtrol tank and 1 with a non-UL plumbing expansion tank. The system

RE: Question Regarding Antifreeze Systems

2011-11-29 Thread Matt Mueller
[mailto:edvinin...@gmail.com] Sent: Monday, November 28, 2011 9:52 AM To: sprinklerforum@firesprinkler.org Subject: Re: Question Regarding Antifreeze Systems I see it is listed down to 40 F. Will the strainer not trap water? Ed Vining 4819 John Muir Rd Martinez CA 94553 925-228-8792 Cell 787-0465 On Mon

RE: Question Regarding Antifreeze Systems

2011-11-28 Thread Frank Herrick
@firesprinkler.org Subject: RE: Question Regarding Antifreeze Systems The problem with not filling an AF system completely is that the air will leak out and be replaced by water from the supply, diluting the mix at the service entrance, which then eventually dissipates and brings the original protection

Re: Question Regarding Antifreeze Systems

2011-11-28 Thread Ed Vining
Lives, Property, the Environment, and Water - Protect what you value most! -Original Message- From: George Church [mailto:g...@rowesprinkler.com] Sent: Sunday, November 20, 2011 8:06 AM To: sprinklerforum@firesprinkler.org Subject: RE: Question Regarding Antifreeze Systems

RE: Question Regarding Antifreeze Systems

2011-11-20 Thread George Church
...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ed Vining Sent: Saturday, November 19, 2011 10:46 PM To: sprinklerforum@firesprinkler.org Subject: Re: Question Regarding Antifreeze Systems I throw this out for comment. This comes a bit late, but I wonder if it is necessary

Re: Question Regarding Antifreeze Systems

2011-11-19 Thread Ed Vining
I throw this out for comment. This comes a bit late, but I wonder if it is necessary to completely fill the system. There is always some air trapped in wet pipe systems, and I wonder how much is too much. Of course the system should be pressurized to above supply pressure. If it were

Question Regarding Antifreeze Systems

2011-11-09 Thread DJJ8389
I am looking to pump Propylene Glycol into a sprinkler system. The only problem is the system feeds an attic about 40 feet high and not very accessible. The capacity is about 100 gallons. Can anybody suggest a pump or method of completing this job? -- next part -- An