Subject: RE: Radio Station Broadcast Studios
Thanks Dick,
Good idea.
Did you know there is a company in Seabrook, NH that makes Retractable
sprinkler heads just for sound proof chambers?
http://www.ramayes.com/Retractable_Telescoping_Sprinkler_Head.htm
How about the Retractable Telescoping sprinkler head designed for anechoic
chambers? See http://www.ramayes.com/Retractable_Telescoping_Sprinkler_Head.htm
Tony Gumkowski, PE
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
CPVC? Cover the pipe with carpet?
At 03:20 PM 6/14/2012, you wrote:
An architect has contacted me concerning remodeling of an existing radio
station.
They have broadcast studios which are isolated double walls which are
structurally independent of the building framing in order to isolate any
Yes, when I was an AHJ. There was little debate, sprinklers got added. I
imagine I offered for them to come up with an equivalency. I suppose they
could use some sort of clean agent but IMHO that's not completely equivalent.
Back then you couldn't omit sprinkler for them and still call a
, 2012 3:29 PM
To: 'sprinklerforum@firesprinkler.org'
Subject: RE: Radio Station Broadcast Studios
How about the Retractable Telescoping sprinkler head designed for
anechoic chambers? See
http://www.ramayes.com/Retractable_Telescoping_Sprinkler_Head.htm
Tony Gumkowski, PE
-Original
...@rowesprinkler.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of G. Tim Stone
Sent: Thursday, June 14, 2012 3:48 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Radio Station Broadcast Studios
Toni
...@firesprinkler.org] On Behalf Of G. Tim Stone
Sent: Thursday, June 14, 2012 3:48 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Radio Station Broadcast Studios
Toni,
Do you represent the company that makes these retractable sprinkler heads?
Regards,
G. Tim Stone
G. Tim Stone
To: sprinklerforum@firesprinkler.org
Subject: Re: Radio Station Broadcast Studios
CPVC? Cover the pipe with carpet?
At 03:20 PM 6/14/2012, you wrote:
An architect has contacted me concerning remodeling of an existing
radio station.
They have broadcast studios which are isolated double walls
: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Greg McGahan
Sent: Thursday, June 14, 2012 3:58 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Radio Station Broadcast Studios
Transition to cpvc and back to steel or just use cpvc.
Greg
Sent from
Hey Tim
We did a recording studio for Mutt Lang and Shania Twain over in Bay
Pond NY. The studio was floating, double wall and triple pane opposing
glass. We used a rubber braided connection rated for the sprinkler system
which stopped any transfer of sound from outside to
...@firesprinkler.org [mailto:sprinklerforum-
boun...@firesprinkler.org] On Behalf Of Dick Culver
Sent: Thursday, June 14, 2012 4:27 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Radio Station Broadcast Studios
Hey Tim
We did a recording studio for Mutt Lang and Shania Twain over
Ladies/Gentlemen:
We have a local public broadcast station here at the community college in
Santa Fe - As best I can tell, standard steel pipe/ cast iron fittings w/SR
pendent sprinklers two-pc. escutcheons 'dangling' from the ceiling - the only
restriction that has been placed on our firm
: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-
boun...@firesprinkler.org] On Behalf Of accentf...@aol.com
Sent: Thursday, June 14, 2012 5:03 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Radio Station Broadcast Studios Suggestion
Ladies/Gentlemen:
We have a local public
To: sprinklerforum@firesprinkler.org
Subject: Re: Radio Station Broadcast Studios Suggestion
Ladies/Gentlemen:
We have a local public broadcast station here at the community college
in Santa Fe - As best I can tell, standard steel pipe/ cast iron
fittings w/SR pendent sprinklers two-pc. escutcheons
A story I have repeated often. Sometime after Adam was kicked out of Eden
KQED TV in San Francisco had an event. Fairly new preaction system.
Normally energized solenoid to trip double interlocked system. Battery
backup for the system. Power failure lasting some time. Person on duty
hears
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Thursday, June 14, 2012 6:15 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Radio Station Broadcast Studios Suggestion
I think you need a diesel fire pump too.
On Thu, Jun 14, 2012 at 2:21 PM, G. Tim Stone tston
i don't get it yet Ed. luckily it is after hours so i don't have to.
Are the 2 key points normally energized and all but 1 link knocked
out?
Quoting Ed Vining edvinin...@gmail.com:
A story I have repeated often. Sometime after Adam was kicked out of Eden
KQED TV in San Francisco had an
A double-interlock preaction with open sprinks? How did the air pressure
part of that work?
Ed Kramer
Manhattan, KS
A story I have repeated often. Sometime after Adam was kicked out of
Eden KQED TV in San Francisco had an event. Fairly new preaction
system.
Normally energized solenoid to
I've heard Ed's story many times and don't know how hos particular DI
worked but although charged air in the system is a common DI arrangement
it's not the only way. An electric detection system plus a pneumatic pilot
line would qualify as DI. DI just requires two distinct events to release
water.
Right. When the batteries died the system tripped. If the contractor had
left the sprinks intact, it would have been just another maintenance call.
The sprink they failed to neuter was just a clue which made me believe it
wasn't deliberately a deluge system. The important thing though, is the