If the manufacturing occupancy has no flammable liquids, no shielded
areas, and no other factors that wiuld prevent quick suppression, then
there would be no reason to increase the design area. But those are very
big ifs and you're asking the AHJ to make the leap of faith to accept
the situation. If the occupancy requires a 2000 sq.ft. design area,
then you're going to need to be prepared for the possibility that 20
sprinklers will operate. You don't, however, need to have the full
pressure required by the building height. K14 ESFRs at 10 X 10 spacing
will get a good distribution pattern at 25 psi.. so, 20 sprinklers at
25 psi would certainly be better than OH protection.
The fundamental problem is that ESFRs are purely storage sprinklers, and
have never been evaluated in any way for control-mode bperformance.
Joe
John Powell wrote:
We have an issue with ESFR in a rack storage area interspersed with
componant assembly. The assembly process does not involve flamable
liquids or hydraulic equipment. There are no shielded hazards and the
storage complies with the ESFR listing. Our AHJ requires that the
limited assembly/process hazard be listed for QR sprinklers, which it
is, and the number of ESFR sprinklers calculated for the usual OH area
of operation discharging at the listed pressure for the storage and
building height involved. Seems excessive to me. Have the forum
members had any similar ruling?
John Powell - New Zealand