If the manufacturing occupancy has no flammable liquids, no shielded areas, and no other factors that wiuld prevent quick suppression, then there would be no reason to increase the design area. But those are very big ifs and you're asking the AHJ to make the leap of faith to accept the situation. If the occupancy requires a 2000 sq.ft. design area, then you're going to need to be prepared for the possibility that 20 sprinklers will operate. You don't, however, need to have the full pressure required by the building height. K14 ESFRs at 10 X 10 spacing will get a good distribution pattern at 25 psi.. so, 20 sprinklers at 25 psi would certainly be better than OH protection.

The fundamental problem is that ESFRs are purely storage sprinklers, and have never been evaluated in any way for control-mode bperformance.

Joe

John Powell wrote:

We have an issue with ESFR in a rack storage area interspersed with componant assembly. The assembly process does not involve flamable liquids or hydraulic equipment. There are no shielded hazards and the storage complies with the ESFR listing. Our AHJ requires that the limited assembly/process hazard be listed for QR sprinklers, which it is, and the number of ESFR sprinklers calculated for the usual OH area of operation discharging at the listed pressure for the storage and building height involved. Seems excessive to me. Have the forum members had any similar ruling?
John Powell - New Zealand
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to