I had been told by one elevator inspector that there was an FM approved
hydraulic media that was non-combustible and if that was being used the
sprinkler in the pit could be deleted.  

On the other hand in another jurisdiction I was told that regardless of
the hydraulic media used that we were to provide a sprinkler in the pit
due to the possible accumulation of miscellaneous debris which could
catch fire.


Isn't it wonderful to be in an industry where everything is so black and
white?   ;)



Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George
Church
Sent: Monday, January 08, 2007 10:41 AM
To: [email protected]
Subject: RE: hydraulic elevators

Perhaps everyone else in the area installs to #13R ?
Perhaps a call to the local AHJ(s) would clear up whether you're the
only one doing it correctly, in which case maybe your competitors will
be a little dismayed to find themselves going back and retrofitting
their bottoms. The call to the AHJ(s) could be two-fold: ask them if
they believe it should be required; and ask WHY it is not- you may find
in the near future you're no longer alone in the shaft.

George Church
Rowe Sprinkler

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of David de
Vries/Firetech
Sent: Monday, January 08, 2007 10:30 AM
To: [email protected]
Subject: Re: hydraulic elevators

Pat on the back to the only contractor in the area complying with this
provision of 13.

--
David de Vries, P.E., CSP
[EMAIL PROTECTED]

-------------- Original message --------------
From: "Greg McGahan" <[EMAIL PROTECTED]> 

> 
> We are receiving mixed reviews from AHJ's regarding this issue: Are 
> sprinklers required in the bottom of hydraulic elevator shafts?
> 
> I know what the code says but we have never been able to document that

> ANY

> hydraulic elev fluid is non-combustible by definition. I was informed 
> this

> morning that we are the only contractor in the area putting sprinklers

> in the bottom of these shafts.
> 
> Thanks,
> Greg McGahan
> 
> 
> 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to