No restrictions that I am aware of.
If memory serves me right, FM made an earlier statement that
localized upright ESFR sprinklers could be used within an otherwise
pendent ESFR system. That had to break the heart of the mfg that
developed the first upright (since they are far superior in regard to
obstructions).
Joe - any comments?
Roland
On Jan 25, 2007, at 9:31 AM, Dan Arbel wrote:
Dear All,
What is your opinion regarding the use of upright and pendent ESFR
sprinklers in the same area?
What about mixing brands of different manufacturers?
Dan