Roland,

You're right. FM did a fire test with ignition centered between a pendant and an upright, and it worked fine.

Uprights are significantly more tolerant of obstructions than pendants, but they are significantly less effective against a fire. The maximum protection comes with unobstructed pendants. The minimum tolerable comes with pendants.

Anyone designing with uprights simply because it's easier to not worry about obstructions needs to remember that he is not getting the same protection he would if he used pendants and avoided obstructions. It's another one of those decisions that designers make without the building owner knowing that he's getting less for his money in the long run in exchange for making the designer's life easier.

There is no such thing as a free lunch!

Joe

Roland Huggins wrote:

No restrictions that I am aware of.

If memory serves me right, FM made an earlier statement that localized upright ESFR sprinklers could be used within an otherwise pendent ESFR system. That had to break the heart of the mfg that developed the first upright (since they are far superior in regard to obstructions).

Joe - any comments?

Roland

On Jan 25, 2007, at 9:31 AM, Dan Arbel wrote:


Dear All,

What is your opinion regarding the use of upright and pendent ESFR
sprinklers in the same area?

What about mixing brands of different manufacturers?

Dan





Dan Arbel Risk Eng
T:  +972 (04) 8243337
F:  +972 (04) 8243278
M: +972 (052) 2810593



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to