Check the roof pitch, over 2 in 12 is forbidden for storage. Sometimes
the Architect's don't check NFPA 13 to determine the roof pitch in a
storage occupancy.

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Lindner,
Richard
Sent: Tuesday, February 06, 2007 10:43 AM
To: [email protected]
Subject: Determining a Warehouse Commodity Classification

(I seem to have lost access to the archives, so I can't research this..)

I am involved in an initial design (performance spec) for a warehouse
type project consisting of a butler building approx. 300'x60' and 35'
high in size (18,000 sq. ft.).  Approx 7000 sq. ft. of floor area will
consist of 25' high rack storage that is 42" deep with a 12" space and
then another 42" deep rack.  There are 5 racks of this arrangement with
an aisle at minimum 9'-6" width between them.  The shelving itself is
wire decking.

The center part of the building has some administrative area offices and
other storage areas (no shelving shown).  The other end of the building
is a maintenance garage for repairs of vehicles.

We have asked about what they intend to store on the shelving and have
been told that primarily they are storing spare machinery parts, some of
which are in wood crates; these are small, medium, large and very large.
These include hydraulic cylinders, engines, transmissions, radiators,
air chambers, pumps, belts, hoses, fittings, nuts, bolts (small items
are in cardboard boxes in most cases), and tools (both power and
non-power tools).  Aerosol cans include brake cleaner, starting fluid,
lubricant (WD-40), window cleaner, and paint.  They carry no more than
two cases (24 cans) of each item in stock.  There are filters, including
fuel, oil, air, water, and hydraulic types, all sizes and shapes.  They
also store spare pre-charged batteries. These are heavy equipment
batteries; (2) large, (2) medium and (4) small are typically all they
have on hand.

We feel the rack storage area is our most demanding area.  We have
reviewed our options and feel that Commodity Class II would be
appropriate based on the above information.  Does anyone see something
that might reflect using a different classification?

Appreciate any response.

Richard
 
Richard K. Lindner
Plumbing Senior Designer
Morris, Johnson & Associates, Inc.
 
611 Industrial Way West
Eatontown, New Jersey  07724
P:  732-380-1100 ext. 4186  |  F:  732-380-1111
[EMAIL PROTECTED] www.morrisjohnson.com 

 
 
 
--------------------------------------------------------

This message contains confidential information and is intended only for
the individual named. If you are not the named addressee you should not
disseminate, distribute or copy this e-mail. Please notify the sender
immediately by e-mail if you have received this e-mail by mistake and
delete this e-mail from your system. E-mail transmission cannot be
guaranteed to be secure or error-free as information could be
intercepted, corrupted, lost, destroyed, arrive late or incomplete, or
contain viruses. The sender therefore does not accept liability for any
errors or omissions in the contents of this message, which arise as a
result of e-mail transmission. If verification is required please
request a hard-copy version.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum