Where is this found? We're on 1999 NFPA 13 and 2000 IBC with NJ enhancments. I checked the design for the structure and it's 1:12 (something is going my way on this project for once??) <s>
Richard K. Lindner Plumbing Senior Designer Morris, Johnson & Associates, Inc. 611 Industrial Way West Eatontown, New Jersey 07724 P: 732-380-1100 ext. 4186 | F: 732-380-1111 [EMAIL PROTECTED] www.morrisjohnson.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] Behalf Of Fletcher, Ron Sent: Tuesday, February 06, 2007 4:31 PM To: [email protected] Subject: RE: Determining a Warehouse Commodity Classification Check the roof pitch, over 2 in 12 is forbidden for storage. Sometimes the Architect's don't check NFPA 13 to determine the roof pitch in a storage occupancy. Ron Fletcher Aero Automatic Sprinkler Phoenix, AZ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum