OK...

I have to say that I have learned a thing or two in this thread...but
for most of it I keep thinking like a code consultant......somebody tell
me I am wrong but....

IBC requires a Class III standpipe for buildings over 30 ft above the
lowest level of FD access.  Since the building is sprinklered, the Class
III requirement is now a Class I requirement due to the IBC exception
#1.

Now, at 6 stories, the walking surface (floor level) of the 6th floor is
almost always less than 75 ft above the lowest level of FD access....a
non high rise.

Now you go to NFPA 14 5.4 permits manual standpipes for this type of
installation...even if in combination with a sprinkler system (See NFPA
14 7.7.3).  The only "automatic" requirement in the building code is for
Group A occupancies and NFPA 14 only requires it for high rises

Bottom line, you can rely on the FD pumper to provide adequate pressure
to the top floor....not your fire sprinkler system fire pump.  This
usually reduces the size of the fire pump considerably and eliminates
the issue of having a pump capable of providing min 100 psi at 750-1000
gpm some 65 ft. up while still maintaining system pressure below 175 at
the lowest levels at churn.

Am I missing something here?  I will not say that this logic always
works as site conditions can make this a closer call.  But an FD pumper
pumping at 175 psi should have no trouble overcoming the 65 ft (30 psi)
elevation loss and any friction losses with some room to spare.

Paul Sincaglia, P.E.