Forum,

I think variations of this topic have been mentioned before but I must apologize for not paying attention. This is about tank sizing.

There is an example in the 13 appendix for determining the design area when the higher hazard type is in a room with walls good for at least the water duration for the higher hazard type. For that condition the design area for the lower hazard type is used to encompass both spaces. The appropriate application density for the larger hazard is used for the larger hazard area and appropriate application density for the lesser hazard is used for the balance of the total design area in the lower hazard space that is outside the walls of the higher hazard space. Now you have probably guessed where this question is going. Since the total Design Area to be used is that of the lesser hazard, does that also mean the Design Duration for the lesser hazard applies to both hazard areas? The question seems silly here but there is a glimmer of possibility in the language used in the NFPA 13. This would mean 30 minutes for each space application where the hazards are LH and OH2. My own thinking would be 60 minutes for the OH2 portion and 30 minutes for the LH portion when the required durations are 60 and 30. When space and budget are tight the difference is significant when it boils down to 13 according to Hoyle versus opinion and there is this BlueBird sized shape parked somewhere in the building.

Thanks,
Allan Seidel
St. Louis, MO _______________________________________________