This is from the 2007 edition of NFPA #20.

5.19.3.4 Pipe Size. The pipe size shall be in accordance with one of the
following two methods: 

(1)      Where the pipe between the hose valve header and connection to the
pump discharge pipe is over 15 ft (4.5 m) in length, the next larger pipe
size than required by 5.19.3.1.3 shall be used. 

(2)*      This pipe is permitted to be sized by hydraulic calculations based
on a total flow of 150 percent of rated pump capacity, including the
following:                                                         

(a)      This calculation shall include friction loss for the total length
of pipe plus equivalent lengths of fittings, control valve, and hose valves,
plus elevation loss, from the pump discharge flange to the hose valve
outlets. 

(b)      The installation shall be proven by a test flowing the maximum
water available. 


I just calculated a test header located approx. 65' from a 750 gpm pump and
it seems to work easily with 6" pipe flowing 1,125 gpm in lieu of increasing
the pipe to 8". Has anyone got experience using this method?

Space is the issue and 6" works much better then 8" in this situation.