I'm pretty sure the language (and intent) of NFPA 13 and manufacturer's listings of these types of sprinklers is that you calculate 5 sprinklers minimum, or the area/density method whichever is greater. So if you have standard sprinklers in compartments that are not fire or area-separated from the larger EC-protected spaces, then the paper walls between them are transparent and I would calc' all of the sprinklers in the most hydraulically demanding area, including EC's and spray sprinklers.
Steve Leyton Protection Design & Consulting -----Original Message----- From: Kathy Tyler [mailto:[EMAIL PROTECTED] Sent: Thursday, March 08, 2007 8:24 AM To: [email protected] Subject: Extended Cov. Hds Calc Area Good Morning Forum, I am currently reviewing a project which is utilizing the Tyco EC-11 extended coverage pendent heads. I have rarely used them and could use your great input. My question is: The calculation area is a kitchen and in the center of the kitchen are three rooms, toilet,offices (which have 5.6 heads in them) the calculation area for the ext. cov. pendents includes these rooms, put are being omitted per 14.4.4.4.2. Can or should the calculation area include these rooms as square footage or should you exclude them and pick up square footage from the areas which have ext. cov. hds? Thank you in advance for all help, Kathryn Kathryn A. Tyler NICET IV, ASCET Member fire protection designer Kelly-Wright & Associates PC Hvac, Plumbing & Fire Protection (520) 887-1919 ext. 302 fax: (520) 696-0280 [EMAIL PROTECTED] <blocked::mailto:[EMAIL PROTECTED]> www.kwmech.com <blocked::http://www.kwmech.com/> _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
