I'm pretty sure the language (and intent) of NFPA 13 and manufacturer's 
listings of these types of sprinklers is that you calculate 5 sprinklers 
minimum, or the area/density method whichever is greater.   So if you have 
standard sprinklers in compartments that are not fire or area-separated from 
the larger EC-protected spaces, then the paper walls between them are 
transparent and I would calc' all of the sprinklers in the most hydraulically 
demanding area, including EC's and spray sprinklers.

Steve Leyton
Protection Design & Consulting

-----Original Message-----
From: Kathy Tyler [mailto:[EMAIL PROTECTED]
Sent: Thursday, March 08, 2007 8:24 AM
To: [email protected]
Subject: Extended Cov. Hds Calc Area


Good Morning Forum,  I am currently reviewing a project which is
utilizing the Tyco EC-11 extended coverage pendent heads.  I have rarely
used them and could use your great input.  
My question is: 
The calculation area is a kitchen and in the center of the kitchen are
three rooms, toilet,offices (which have 5.6 heads in them) the
calculation area for the ext. cov. pendents includes these rooms, put
are being omitted per 14.4.4.4.2.  Can or should the calculation area
include these rooms as square footage or should you exclude them and
pick up square footage from the areas which have ext. cov. hds?
Thank you in advance for all help,
Kathryn
 
Kathryn A. Tyler NICET IV, ASCET Member
fire protection designer
Kelly-Wright & Associates PC
Hvac, Plumbing & Fire Protection
(520) 887-1919 ext. 302
fax: (520) 696-0280
[EMAIL PROTECTED] <blocked::mailto:[EMAIL PROTECTED]> 
www.kwmech.com <blocked::http://www.kwmech.com/> 
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to