From: "Travis Mack" <[EMAIL PROTECTED]>
Reply-To: [email protected]
To: <[email protected]>
Subject: RE: Extended Cov. Hds Calc Area
Date: Thu, 8 Mar 2007 09:41:58 -0700
Kathryn:
The EC-11 are not QR in OH applications. They are SR. Therefore,
the QR
reduction does not apply.
As far as:
"Ok I need to add one more question to the omission of these three
rooms per
14.4.4.4.2 2002 edition, it states 'closets, washrooms, & similar small
compartments requiring only one head' --- The rooms are a toilet,
break room
and an office - I am willing to allow the omission of using the
toilet but
the other two I do not believe they are what NFPA's intent was to omit.
What do you all think?"
I think the other similar compartments requiring only 1 head would
allow the
heads in the office / breakroom to be omitted. I thought there was
something on here about 2 years ago about this situation and it was
basically the "requiring only one head" was the trump card. I don't
think
it would apply in a mech room or anything really different than light
hazard.
Travis
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
Kathryn Tyler
Sent: Thursday, March 08, 2007 9:40 AM
To: [email protected]
Subject: RE: Extended Cov. Hds Calc Area
EXCELLENT!!! Brian - it sure would qualify, Thank you very much I did
not
even consider that, it will allow ext. cov to be reduced also.
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Thursday, March 08, 2007 9:32 AM
To: [email protected]
Subject: RE: Extended Cov. Hds Calc Area
Just to be safe on the 1500 sq.ft., is area reduction applicable?
Regards,
Brian Harris
First Defense Fire Protection
Design Engineer
[EMAIL PROTECTED]
704.948.3506 phone
704.948.3507 fax
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
Kathryn Tyler
Sent: Thursday, March 08, 2007 11:30 AM
To: [email protected]
Subject: RE: Extended Cov. Hds Calc Area
Anyone else with different or the same thoughts as Steve?
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
Kathryn Tyler
Sent: Thursday, March 08, 2007 9:27 AM
To: [email protected]
Subject: RE: Extended Cov. Hds Calc Area
The 5 sprinklers are not the greater, so the 1500 sq. ft. is having
to be
used. So include those rooms, I thought that would be true, they are not
demising walls. Thank u
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve
Leyton
Sent: Thursday, March 08, 2007 9:20 AM
To: [email protected]
Subject: RE: Extended Cov. Hds Calc Area
I'm pretty sure the language (and intent) of NFPA 13 and manufacturer's
listings of these types of sprinklers is that you calculate 5 sprinklers
minimum, or the area/density method whichever is greater. So if you
have
standard sprinklers in compartments that are not fire or
area-separated from
the larger EC-protected spaces, then the paper walls between them are
transparent and I would calc' all of the sprinklers in the most
hydraulically demanding area, including EC's and spray sprinklers.
Steve Leyton
Protection Design & Consulting
-----Original Message-----
From: Kathy Tyler [mailto:[EMAIL PROTECTED]
Sent: Thursday, March 08, 2007 8:24 AM
To: [email protected]
Subject: Extended Cov. Hds Calc Area
Good Morning Forum, I am currently reviewing a project which is
utilizing
the Tyco EC-11 extended coverage pendent heads. I have rarely used
them and
could use your great input.
My question is:
The calculation area is a kitchen and in the center of the kitchen
are three
rooms, toilet,offices (which have 5.6 heads in them) the calculation
area
for the ext. cov. pendents includes these rooms, put are being
omitted per
14.4.4.4.2. Can or should the calculation area include these rooms as
square footage or should you exclude them and pick up square footage
from
the areas which have ext. cov. hds?
Thank you in advance for all help,
Kathryn
Kathryn A. Tyler NICET IV, ASCET Member
fire protection designer
Kelly-Wright & Associates PC
Hvac, Plumbing & Fire Protection
(520) 887-1919 ext. 302
fax: (520) 696-0280
[EMAIL PROTECTED] <blocked::mailto:[EMAIL PROTECTED]>
www.kwmech.com <blocked::http://www.kwmech.com/>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
--
No virus found in this incoming message.
Checked by AVG Free Edition.
Version: 7.5.446 / Virus Database: 268.18.8/714 - Release Date: 3/8/2007
10:58 AM
--
No virus found in this outgoing message.
Checked by AVG Free Edition.
Version: 7.5.446 / Virus Database: 268.18.8/714 - Release Date: 3/8/2007
10:58 AM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum