Thank you my thoughts exactly concerning the rooms.  I welcome any more
comments, but extend thanks to all.
Kathryn
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jarrod
Poorman
Sent: Thursday, March 08, 2007 9:51 AM
To: [email protected]
Subject: Re: Extended Cov. Hds Calc Area

If you omit the sprinkler heads allowed in 14.4.4.4.2, you cannot use the
design area reduction.  You have to calc to 1500 sqft even if QR 
heads are used.   If you have the handbook, it goes into further 
explanation. 

In addition, 14.4.4.4.2 applies to small the rooms with small fuel loads.
Offices and such have higher fuel loads that and regular closet or bathroom.
That is why you can omit heads from closets and bathrooms, but not offices.


Jarrod Poorman
Sr. Fire Protection Design Technician
Global Fire Engineering
www.global-fire.com
Office (941)-758-2551
Fax (941)-739-6383



Kathryn Tyler wrote:
> Of course whichever is greater the 900 sq ft or 5 heads... 
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Kathryn 
> Tyler
> Sent: Thursday, March 08, 2007 9:40 AM
> To: [email protected]
> Subject: RE: Extended Cov. Hds Calc Area
>
> EXCELLENT!!! Brian - it sure would qualify, Thank you very much I did 
> not even consider that, it will allow ext. cov to be reduced also.
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Brian 
> Harris
> Sent: Thursday, March 08, 2007 9:32 AM
> To: [email protected]
> Subject: RE: Extended Cov. Hds Calc Area
>
> Just to be safe on the 1500 sq.ft., is area reduction applicable?
>
>            Regards,
>               Brian Harris
> First Defense Fire Protection
>         Design Engineer
>    [EMAIL PROTECTED]
>            704.948.3506 phone
>            704.948.3507 fax
>
>  
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Kathryn 
> Tyler
> Sent: Thursday, March 08, 2007 11:30 AM
> To: [email protected]
> Subject: RE: Extended Cov. Hds Calc Area
>
> Anyone else with different or the same thoughts as Steve? 
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Kathryn 
> Tyler
> Sent: Thursday, March 08, 2007 9:27 AM
> To: [email protected]
> Subject: RE: Extended Cov. Hds Calc Area
>
> The 5 sprinklers are not the greater, so the 1500 sq. ft. is having to 
> be used. So include those rooms, I thought that would be true, they 
> are not demising walls. Thank u
>   
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Steve 
> Leyton
> Sent: Thursday, March 08, 2007 9:20 AM
> To: [email protected]
> Subject: RE: Extended Cov. Hds Calc Area
>
> I'm pretty sure the language (and intent) of NFPA 13 and 
> manufacturer's listings of these types of sprinklers is that you calculate
5 sprinklers
> minimum, or the area/density method whichever is greater.   So if you have
> standard sprinklers in compartments that are not fire or 
> area-separated from the larger EC-protected spaces, then the paper 
> walls between them are transparent and I would calc' all of the 
> sprinklers in the most hydraulically demanding area, including EC's and
spray sprinklers.
>
> Steve Leyton
> Protection Design & Consulting
>
> -----Original Message-----
> From: Kathy Tyler [mailto:[EMAIL PROTECTED]
> Sent: Thursday, March 08, 2007 8:24 AM
> To: [email protected]
> Subject: Extended Cov. Hds Calc Area
>
>
> Good Morning Forum,  I am currently reviewing a project which is 
> utilizing the Tyco EC-11 extended coverage pendent heads.  I have 
> rarely used them and could use your great input.
> My question is: 
> The calculation area is a kitchen and in the center of the kitchen are 
> three rooms, toilet,offices (which have 5.6 heads in them) the 
> calculation area for the ext. cov. pendents includes these rooms, put 
> are being omitted per 14.4.4.4.2.  Can or should the calculation area 
> include these rooms as square footage or should you exclude them and 
> pick up square footage from the areas which have ext. cov. hds?
> Thank you in advance for all help,
> Kathryn
>  
> Kathryn A. Tyler NICET IV, ASCET Member fire protection designer 
> Kelly-Wright & Associates PC Hvac, Plumbing & Fire Protection
> (520) 887-1919 ext. 302
> fax: (520) 696-0280
> [EMAIL PROTECTED] <blocked::mailto:[EMAIL PROTECTED]>
> www.kwmech.com <blocked::http://www.kwmech.com/>
>  
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
> .
>
>   
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to