The 5 sprinklers are not the greater, so the 1500 sq. ft. is having to be
used. So include those rooms, I thought that would be true, they are not
demising walls. Thank u
  

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton
Sent: Thursday, March 08, 2007 9:20 AM
To: [email protected]
Subject: RE: Extended Cov. Hds Calc Area

I'm pretty sure the language (and intent) of NFPA 13 and manufacturer's
listings of these types of sprinklers is that you calculate 5 sprinklers
minimum, or the area/density method whichever is greater.   So if you have
standard sprinklers in compartments that are not fire or area-separated from
the larger EC-protected spaces, then the paper walls between them are
transparent and I would calc' all of the sprinklers in the most
hydraulically demanding area, including EC's and spray sprinklers.

Steve Leyton
Protection Design & Consulting

-----Original Message-----
From: Kathy Tyler [mailto:[EMAIL PROTECTED]
Sent: Thursday, March 08, 2007 8:24 AM
To: [email protected]
Subject: Extended Cov. Hds Calc Area


Good Morning Forum,  I am currently reviewing a project which is utilizing
the Tyco EC-11 extended coverage pendent heads.  I have rarely used them and
could use your great input.  
My question is: 
The calculation area is a kitchen and in the center of the kitchen are three
rooms, toilet,offices (which have 5.6 heads in them) the calculation area
for the ext. cov. pendents includes these rooms, put are being omitted per
14.4.4.4.2.  Can or should the calculation area include these rooms as
square footage or should you exclude them and pick up square footage from
the areas which have ext. cov. hds?
Thank you in advance for all help,
Kathryn
 
Kathryn A. Tyler NICET IV, ASCET Member
fire protection designer
Kelly-Wright & Associates PC
Hvac, Plumbing & Fire Protection
(520) 887-1919 ext. 302
fax: (520) 696-0280
[EMAIL PROTECTED] <blocked::mailto:[EMAIL PROTECTED]>
www.kwmech.com <blocked::http://www.kwmech.com/> 
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to