I am reviewing a dry system attic layout using Tyco's Single Directional (SD) and Back to Back (BB) attic heads. The attic narrows at the remote area so that the peak goes from an attic peak (12/4 slope)with roof on each side, to a roof only on one side of the peak. (sorry for the poor description, it would make sense if you could look at the plan).
What is important to my question is that the 3 most remote heads are SD heads and then it continues with BB's along the peak. The cut sheets on these specific application sprinklers say when you have BB's and SD's to calculate the 7 most demanding BB sprinklers plus up to 2 SD sprinklers. But, the example figure shows a little different scenario than what I have. The technician who laid this out calc'd the 7 most remote sprinklers (3 SD's and 4 BB's). I'm thinkin' that is not right. It looks to me as though the 7 most remote BB's and the adjacent 2 SD's should be calc'd. Maybe we are both wrong?? Any guidance will be appreciated. Reed A. Roisum Fire Protection Technician Ulteig Engineers, Inc. 3350 38th Avenue South Fargo, ND 58104-7079 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum