What is supposed to happen and what may happen can be two completely
different things. And as Russ points out in his #25 Seminar, when you do a
lot of work, it's not a matter of IF something will happen, but WHEN
something does happen.

We upgraded the supply for an ex industrial building for a new addition with
K25's at 60 PSI, new diesel pump, ex 8" loop. Due to the one addition with
the high flow being around the back, we ended up with a system we knew would
be about 175 at normal settings, but ends up sitting- with the permission of
the AHJ and Owner- at 180~ 185 PSI.

Prior to installing the fire pump, we went in and hydro'd the 6 existing
(circa 1968 thru 1985+/-) systems with the written agreement that the owner
was responsible for water damage resulting from us testing HIS existing
systems.

The repairs took about 20 minutes total for all 6 systems- band on a couple
grooved couplings, take a couple lines a turn around, and tighten the
packing on an ITC valve. No big deal.

Once the pump was installed we did discover (well, maybe "create" would be
more descriptive) a handful of UG leaks which were dug up and replaced. But
overall, there was a lot more potential for damage and expense than
occurred. But the understanding was very simple- the OWNER had liability for
what happened to HIS system when we tested it at high pressure (which was
250 PSI, btw). 

We are blessed that this Owner is both extremely knowledgeable in sprinklers
and pumps, and understands and applies fairness in contracting. Heck, they
even pay within 30 days, and want SCV's around a loop where they make sense,
just like the good old days of HPR accounts being protected appropriate to
their risk and value, rather than to the cheapest interpretation of minimum
concensus standards.

When you have operations that require K25s at 60 PSI, it is good to
understand what ya got and how to use it. We enjoy the high-testosterone
water supplies, our 2nd project with these guys has another 2500 gpm diesel
on order (different location, not a redundant supply).

So its possible, hopefully probable, that you can test an existing system at
high pressure, but its not necessary, even foolhardy, to think you should
expose yourself or your insurance carrier to the potential losses. Its not
your risk to assume if others installed it and the monkey is on the owner's
back.

glc
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe Hankins
Sent: Thursday, March 08, 2007 10:01 PM
To: [email protected]
Subject: Re: What I'm Hearing About Hydrostatic Testing

There was nothing to suggest water hammer. Water hammer resulting from a 
pump start is unlikely in sprinkler system piping. Even if  there is a 
water hammer problem, it's something you want to know because it's easy 
to fiz.When you do see water hammer from a fire pump, it usually happens 
in underground.

Also, starting fire pumps with the discharge valve open is by far the 
most common way weekly runs are made.  I've seen many sprinkler systems 
that have held up to weekly pump starts for more than 30 years without 
incident.

If you truly beleive that a sprinkler system can be blown apart by a 
fire pump, you have a very low opinion of  the quality of sprinkler 
installations!

Joe