Folks A water hammer can do nasty things to a sprinklers system but just pump pressure can cause problems if the sprinkler fitters have not done their work properly. Years ago at Phillips Plaza in Atlanta a grooved coupling was not properly tightened because the groove on the pipe was too shallow. The grooved coupling held for the 200 psi test but later when the pump was put into service the coupling did not hold and the basement of the upscale mall was flooded and the complete mall was shut down for several hours while the system was repaired. Fortunately the installers were not mine.
Michael L. Brown -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Roland Huggins Sent: Friday, March 09, 2007 10:37 AM To: [email protected] Subject: Re: What I'm Hearing About Hydrostatic Testing more worried about it NOT staying in its intended orientation. Joe - Did you guys see any systems where sprigs and rotated? Roland On Mar 8, 2007, at 7:01 PM, Joe Hankins wrote: > There was nothing to suggest water hammer. Water hammer resulting > from a pump start is unlikely in sprinkler system piping. Even if > there is a water hammer problem, it's something you want to know > because it's easy to fiz.When you do see water hammer from a fire > pump, it usually happens in underground. > > Also, starting fire pumps with the discharge valve open is by far > the most common way weekly runs are made. I've seen many sprinkler > systems that have held up to weekly pump starts for more than 30 > years without incident. > > If you truly beleive that a sprinkler system can be blown apart by > a fire pump, you have a very low opinion of the quality of > sprinkler installations! > > Joe _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum