Chris,
They would have the same effect that any valve or fitting would have on
the ability of a sprinkler system to function properly. The loss in
pressure due to friction at various flows through the meters is required
to be accounted for in the hydraulic calculations. Interestingly
enough, NFPA-13D tells us that the actual chart loss from the meter
manufacturer should be reviewed during the calculation process. If the
chart loss is lower than those figures in the table in 13D it may be
used, however the standard also says that if the chart loss from the
manufacturer is greater than those shown in the table that the higher
value MUST be used.
Out here we see hundreds of residential sprinklers systems every month,
and for the most part they utilize 1" meters. With a 13 gpm demand per
sprinkler, and a 5 gpm allowance for domestic use, the system flow of 31
gpm exceeds the values shown in 13D as acceptable for a 5/8", and is
right on the line at the maximum allowed for a 3/4".
There has been much shouting regarding the issue of meter size out here,
and most of it accompanied by vague suggestions of dire consequences and
thousands of dollars needlessly wasted if one position or another isn't
followed.
What is your take on the issues involved?
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
Chris Brown wrote:
Question to the forum:
What effect does a 5/8 inch or 3/4 inch water meter have on fire sprinkler
system installed in an NFPA 13D or NFPA 13R system. The issue is one of the
maximum continuous flow thru the meter and its effect on the ability of the
fire sprinkler system to operate as intended. I respectfully request, Please
research and answer after you have visited with the water meter manufacturer's
and or water departments as I have already done. Keep in mind that a single
residential sprinkler has a minimum of some where between 19 and 25 gpm
requirements and that most dwellings have two sprinklers flowing in the
hydraulically remote area.
This will be fun for a Friday:)
Thank you,
Chris Brown
Fire Protection Designer
Please note our new company name, e-mail address and web site.
innovative leader $B"%(J trusted partner
19910 West 161st Street
Olathe, KS 66062
Office: 913.829.8650
Direct:
Cell:
Fax:
913.747.2056
913.208.3600
913.829.8690
www.poolefire.com <http://www.poolefire.com/>
Office Map <http://www.mapquest.com/maps/map.adp?address=19910%20W%20161st%20St&city=Olathe&state=KS&zipcode=66062-2700&country=US&title=%3cb%3e19910%20W%20161st%20St%3c/b%3e%3cbr%20/%3e%20Olathe,%20KS%2066062-2700,%20%20US&cid=lfmaplink2&name=>
This e-mail, and any files transmitted with it, are confidential and intended
solely for the use of the individual or entity to which they are addressed. If
you have received this e-mail in error, please notify [EMAIL PROTECTED]
------------------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
------------------------------------------------------------------------
No virus found in this incoming message.
Checked by AVG Free Edition.
Version: 7.5.446 / Virus Database: 268.18.8/714 - Release Date: 3/8/2007 10:58
AM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum