Since this is a test:
1) The meter will have no effect on the operation of the 13D system if you
install it per NFPA 13D, 2007 Figure A.6.2(a) or (b)
or
2) There are no 5/8" meters that will not screw you over bad for pressure
and flow.The only possible hope is you have no rooms with more than 1 head,
and the largest room is no more than 12x12. The 3/4" meters may allow the
Gpm you need but the pressure drop will be excessive. Get the water purveyor
to allow you to by-pass the meter or supply a 1" full port (flow) meter for
13D systems.