Fair enough. Can you then give us an example of how those conclusions, or that information could be applied?

For example, let's say I've designed a sprinkler system in the district you're referring to, and have been told that I have a 3/4" water meter. My system demand is 31.7 gpm. What information do you take from the scenarios you mention and utilize in the calculations? And why?

PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website




Chris Brown wrote:
I have researched this with 2 meter manufacturer's and one water
district. The consensus has been the same with all three. A water meter
as several charts, find a web site, print of the data first. There is
Typical low flow, Typical Operating Range and Maximum Continuous
Operation. The Maximum Continuous Operation of the meters are very
different than the Operating Range of the meter. A fire sprinkler system
would be considered a Continuous Operating feature, I believe this as
does the three people I referred to above.


Thank you,

Chris Brown
Fire Protection Designer, Poole Fire Protection
Office: 913.829.8650   Direct: 913.747.2056   Cell: 913.208.3600   Fax:
913.829.8690


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of PCE
Sent: Friday, March 09, 2007 9:48 AM
To: [email protected]
Subject: Re: Pandora's Box

Chris,

They would have the same effect that any valve or fitting would have on
the ability of a sprinkler system to function properly.  The loss in
pressure due to friction at various flows through the meters is required
to be accounted for in the hydraulic calculations.  Interestingly
enough, NFPA-13D tells us that the actual chart loss from the meter
manufacturer should be reviewed during the calculation process.  If the
chart loss is lower than those figures in the table in 13D it may be
used, however the standard also says that if the chart loss from the
manufacturer is greater than those shown in the table that the higher
value MUST be used.

Out here we see hundreds of residential sprinklers systems every month,
and for the most part they utilize 1" meters.  With a 13 gpm demand per
sprinkler, and a 5 gpm allowance for domestic use, the system flow of 31
gpm exceeds the values shown in 13D as acceptable for a 5/8", and is
right on the line at the maximum allowed for a 3/4".
There has been much shouting regarding the issue of meter size out here,
and most of it accompanied by vague suggestions of dire consequences and
thousands of dollars needlessly wasted if one position or another isn't
followed.

What is your take on the issues involved?

PARSLEY CONSULTING

Ken Wagoner, SET

760.745.6181 voice

760.745.0537 fax

[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail

www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website




Chris Brown wrote:
Question to the forum:
What effect does a 5/8 inch or 3/4 inch water meter have on fire
sprinkler system installed in an NFPA 13D or NFPA 13R system. The issue
is one of the maximum continuous flow thru the meter and its effect on
the ability of the fire sprinkler system to operate as intended. I
respectfully request, Please research and answer after you have visited
with the water meter manufacturer's and or water departments as I have
already done. Keep in mind that a single residential sprinkler has a
minimum of some where between 19 and 25 gpm requirements and that most
dwellings have two sprinklers flowing in the hydraulically remote area.
This will be fun for a Friday:)

Thank you,

Chris Brown
Fire Protection Designer
Please note our new company name, e-mail address and web site.

innovative leader    $B"%(J     trusted partner

19910 West 161st Street
Olathe, KS  66062
Office:  913.829.8650

Direct:
Cell: Fax:

913.747.2056
913.208.3600
913.829.8690

www.poolefire.com <http://www.poolefire.com/> Office Map <http://www.mapquest.com/maps/map.adp?address=19910%20W%20161st%20St&c
ity=Olathe&state=KS&zipcode=66062-2700&country=US&title=%3cb%3e19910%2
0W%20161st%20St%3c/b%3e%3cbr%20/%3e%20Olathe,%20KS%2066062-2700,%20%20
US&cid=lfmaplink2&name=>

This e-mail, and any files transmitted with it, are confidential and
intended solely for the use of the individual or entity to which they
are addressed.  If you have received this e-mail in error, please notify
[EMAIL PROTECTED]
----------------------------------------------------------------------
--

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----------------------------------------------------------------------
--

No virus found in this incoming message.
Checked by AVG Free Edition.
Version: 7.5.446 / Virus Database: 268.18.8/714 - Release Date: 3/8/2007 10:58 AM

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to