If you look at the Hersey Meter 400 Series IIS and 500 Series IIS the flow characteristics are shown and it becomes very clear that a 1" meter would be the minimum size for MOST Dwelling fire sprinkler systems (NOT ALL). Real life example: 2 low flow sprinklers requiring a minimum of 13 GPM calculated has a requirement of 26 GPM at 60 PSI. Given these values my meter will have to be at least 1". How many dwellings have a one inch meter. The cost of a one inch meter in the jurisdiction I'm dealing with is a 1,000.00 dollars more than a standard 5/8 inch by 3/4 inch meter. The use of a meter any larger that that would require a special approval by the water district and the additional cost would be $10,000.00 for a 1 1/2 inch meter.
Given the example presented by Ken would require a one inch meter minimum as the 3/4 inch meter (Hersey) only has a Maximum Continuous Operation of 25 GPM. Thank you, Chris Brown Fire Protection Designer, Poole Fire Protection Office: 913.829.8650 Direct: 913.747.2056 Cell: 913.208.3600 Fax: 913.829.8690 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of PCE Sent: Friday, March 09, 2007 10:34 AM To: [email protected] Subject: Re: Pandora's Box Fair enough. Can you then give us an example of how those conclusions, or that information could be applied? For example, let's say I've designed a sprinkler system in the district you're referring to, and have been told that I have a 3/4" water meter. My system demand is 31.7 gpm. What information do you take from the scenarios you mention and utilize in the calculations? And why? PARSLEY CONSULTING Ken Wagoner, SET 760.745.6181 voice 760.745.0537 fax [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website Chris Brown wrote: > I have researched this with 2 meter manufacturer's and one water > district. The consensus has been the same with all three. A water > meter as several charts, find a web site, print of the data first. > There is Typical low flow, Typical Operating Range and Maximum > Continuous Operation. The Maximum Continuous Operation of the meters > are very different than the Operating Range of the meter. A fire > sprinkler system would be considered a Continuous Operating feature, I > believe this as does the three people I referred to above. > > > Thank you, > > Chris Brown > Fire Protection Designer, Poole Fire Protection > Office: 913.829.8650 Direct: 913.747.2056 Cell: 913.208.3600 Fax: > 913.829.8690 > > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of PCE > Sent: Friday, March 09, 2007 9:48 AM > To: [email protected] > Subject: Re: Pandora's Box > > Chris, > > They would have the same effect that any valve or fitting would have > on the ability of a sprinkler system to function properly. The loss > in pressure due to friction at various flows through the meters is > required to be accounted for in the hydraulic calculations. > Interestingly enough, NFPA-13D tells us that the actual chart loss > from the meter manufacturer should be reviewed during the calculation > process. If the chart loss is lower than those figures in the table > in 13D it may be used, however the standard also says that if the > chart loss from the manufacturer is greater than those shown in the > table that the higher value MUST be used. > > Out here we see hundreds of residential sprinklers systems every > month, and for the most part they utilize 1" meters. With a 13 gpm > demand per sprinkler, and a 5 gpm allowance for domestic use, the > system flow of 31 gpm exceeds the values shown in 13D as acceptable > for a 5/8", and is right on the line at the maximum allowed for a 3/4". > > There has been much shouting regarding the issue of meter size out > here, and most of it accompanied by vague suggestions of dire > consequences and thousands of dollars needlessly wasted if one > position or another isn't followed. > > What is your take on the issues involved? > > PARSLEY CONSULTING > > Ken Wagoner, SET > > 760.745.6181 voice > > 760.745.0537 fax > > [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail > > www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website > > > > > Chris Brown wrote: > >> Question to the forum: >> What effect does a 5/8 inch or 3/4 inch water meter have on fire >> > sprinkler system installed in an NFPA 13D or NFPA 13R system. The > issue is one of the maximum continuous flow thru the meter and its > effect on the ability of the fire sprinkler system to operate as > intended. I respectfully request, Please research and answer after you > have visited with the water meter manufacturer's and or water > departments as I have already done. Keep in mind that a single > residential sprinkler has a minimum of some where between 19 and 25 > gpm requirements and that most dwellings have two sprinklers flowing in the hydraulically remote area. > >> >> This will be fun for a Friday:) >> >> Thank you, >> >> Chris Brown >> Fire Protection Designer >> Please note our new company name, e-mail address and web site. >> >> >> >> innovative leader $B"%(J trusted partner >> >> 19910 West 161st Street >> Olathe, KS 66062 >> Office: 913.829.8650 >> >> Direct: >> Cell: >> Fax: >> >> 913.747.2056 >> 913.208.3600 >> 913.829.8690 >> >> www.poolefire.com <http://www.poolefire.com/> Office Map >> <http://www.mapquest.com/maps/map.adp?address=19910%20W%20161st%20St& >> c >> ity=Olathe&state=KS&zipcode=66062-2700&country=US&title=%3cb%3e19910% >> 2 >> 0W%20161st%20St%3c/b%3e%3cbr%20/%3e%20Olathe,%20KS%2066062-2700,%20%2 >> 0 >> US&cid=lfmaplink2&name=> >> >> This e-mail, and any files transmitted with it, are confidential and >> > intended solely for the use of the individual or entity to which they > are addressed. If you have received this e-mail in error, please > notify [EMAIL PROTECTED] > >> >> >> >> --------------------------------------------------------------------- >> - >> -- >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> >> --------------------------------------------------------------------- >> - >> -- >> >> No virus found in this incoming message. >> Checked by AVG Free Edition. >> Version: 7.5.446 / Virus Database: 268.18.8/714 - Release Date: >> 3/8/2007 10:58 AM >> >> > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum