Charles, Slippery slope. The only reason there is a valve on each side of the BFP is to isolate it for testing. As such those valves are part of the listing of the BFP and cannot be used in the configuration you describe.
On 3/28/07, Haugen, Charles <[EMAIL PROTECTED]> wrote:
Just position it AFTER the tee split, correct? I can see that working as well. -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Eric Shelton Sent: Wednesday, March 28, 2007 1:57 PM To: [email protected] Subject: RE: Riser Schematic vs. InstallationPractices...(sorryifdoubledup...) So, does anyone see why the gate valve on the downstream side of a BFP can't be used as the system isolation valve? Eric Shelton Hankins and Anderson, Inc. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)