You Can if it's only controlling one riser or you want/are allowed to
shut down all risers with one valve. What you can't do is move the
isolation (not control) valve  and add a tee between it and the check
valve to feed the second riser as Chuck described.

On 3/28/07, Roland Huggins <[EMAIL PROTECTED]> wrote:
if the BFP can act as the system check valve, why not use one of its
valves as the required system valve?

Roland

On Mar 28, 2007, at 3:07 PM, Ron Greenman wrote:

> Charles,
>
> Slippery slope. The only reason there is a valve on each side of the
> BFP is to isolate it for testing. As such those valves are part of the
> listing of the BFP and cannot be used in the configuration you
> describe.
>
> On 3/28/07, Haugen, Charles <[EMAIL PROTECTED]> wrote:
>> Just position it AFTER the tee split, correct?  I can see that
>> working
>> as well.
>>
>> -----Original Message-----
>> From: [EMAIL PROTECTED]
>> [mailto:[EMAIL PROTECTED] On Behalf Of Eric
>> Shelton
>> Sent: Wednesday, March 28, 2007 1:57 PM
>> To: [email protected]
>> Subject: RE: Riser Schematic vs.
>> InstallationPractices...(sorryifdoubledup...)
>>
>> So, does anyone see why the gate valve on the downstream side of a
>> BFP
>> can't be used as the system isolation valve?
>>
>> Eric Shelton
>> Hankins and Anderson, Inc.
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email
>> to:[EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email to:Sprinklerforum-
>> [EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>>
>
>
> --
> Ron Greenman
> at home....
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:Sprinklerforum-
> [EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to