We're raising our heads out of the sand of being spkr guys and bidding a manufacturing building (wood and vinyl building products) as ESFR since this eliminates the need for heat and smoke vents, thus more than compensating for the increased cost over OH 2 thru most of the building. There will be some rack storage, but mostly manufacturing.
Without the large fire plume usually associated with rack storage being absent cause a problem with activation of the ESFR? 40' roof, maybe slightly higher (yes, expensive couple of feet possible requiring K25's) Owner is self-insured, generally risk aversive, the now rare breed that actually wants it done "correctly" although money is not to be ignored. We'd like to advise if this could present problems with adequate protection levels. I know this was touched on briefly, but its one of those weird eves when email works but internet doesn't. maybe its on strike in sympathy? George L. Church, Jr. President Rowe Sprinkler Systems, Inc. 7993 US Hwy 522 PO Box 407 Middleburg, PA 17842 570-837-7647 570-837-6335 fax [EMAIL PROTECTED] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)