It is best to check the local building codes used by your AHJ.  Typically,
when the highest floor level above the lowest level of fire dept access is
30' or greater, you will need standpipes.  When the highest floor is >=75',
then you must have an automatic supply for the standpipes.

Again, check the building code and project specific requirements as these
are only guides. 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris
Sent: Thursday, April 12, 2007 7:39 AM
To: [EMAIL PROTECTED]
Subject: RE: Standpipe Question

So unless directed otherwise a building 75' or taller would need a
standpipe, correct?

           Regards,
              Brian Harris
First Defense Fire Protection
        Design Engineer
   [EMAIL PROTECTED]
           704.948.3506 phone
           704.948.3507 fax

 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Thursday, April 12, 2007 10:43 AM
To: [EMAIL PROTECTED]
Subject: RE: Standpipe Question

Your building height as directed in the applicable building code tells you
when you need them, or if specifics of your project require the AHJ, for
access reasons, to treat them as a necessity. I have a 3-story elderly where
the CEO was a volunteer FF and thus wants them added to his job even if not
required by code.

And, what Steve will say.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris
Sent: Thursday, April 12, 2007 10:31 AM
To: [EMAIL PROTECTED]
Subject: Standpipe Question

I recently took a ½ day class on standpipes and have a stupid question to
ask…….

When or what determines if a standpipe is needed? Is it strictly based on a
building being considered high rise (75’) or is there more to it than that?

 

           Regards,

              Brian Harris
First Defense Fire Protection
        Design Engineer

    <mailto:[EMAIL PROTECTED]> [EMAIL PROTECTED]
           704.948.3506 phone
           704.948.3507 fax



 

 


_______________________________________________
Sprinklerforum mailing list
[EMAIL PROTECTED]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[EMAIL PROTECTED]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

--
No virus found in this incoming message.
Checked by AVG Free Edition.
Version: 7.5.446 / Virus Database: 269.2.0/756 - Release Date: 4/10/2007
10:44 PM
 

-- 
No virus found in this outgoing message.
Checked by AVG Free Edition.
Version: 7.5.446 / Virus Database: 269.2.0/756 - Release Date: 4/10/2007
10:44 PM
 

_______________________________________________
Sprinklerforum mailing list
[EMAIL PROTECTED]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to