Don't quote me...Look at your building code...but if you use IBC the
standpipe is required if the top floor is more than 30 ft. above grade

Bottom line-

Get the building code.  Generally speaking it is the building code that
adopts NFPA 14 by reference.  Therefore, any provision contained in the
building code trump base requirements in the NFPA document.

Paul Sincaglia, P.E.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Thursday, April 12, 2007 10:39 AM
To: [EMAIL PROTECTED]
Subject: RE: Standpipe Question

So unless directed otherwise a building 75' or taller would need a
standpipe, correct?

           Regards,
              Brian Harris
First Defense Fire Protection
        Design Engineer
   [EMAIL PROTECTED]
           704.948.3506 phone
           704.948.3507 fax

 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George
Church
Sent: Thursday, April 12, 2007 10:43 AM
To: [EMAIL PROTECTED]
Subject: RE: Standpipe Question

Your building height as directed in the applicable building code tells
you
when you need them, or if specifics of your project require the AHJ, for
access reasons, to treat them as a necessity. I have a 3-story elderly
where
the CEO was a volunteer FF and thus wants them added to his job even if
not
required by code.

And, what Steve will say.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Thursday, April 12, 2007 10:31 AM
To: [EMAIL PROTECTED]
Subject: Standpipe Question

I recently took a ½ day class on standpipes and have a stupid question
to
ask…….

When or what determines if a standpipe is needed? Is it strictly based
on a
building being considered high rise (75’) or is there more to it than
that?

 

           Regards,

              Brian Harris
First Defense Fire Protection
        Design Engineer

    <mailto:[EMAIL PROTECTED]> [EMAIL PROTECTED]
           704.948.3506 phone
           704.948.3507 fax



 

 


_______________________________________________
Sprinklerforum mailing list
[EMAIL PROTECTED]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[EMAIL PROTECTED]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[EMAIL PROTECTED]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to