what kind of pipe?...good question. 
Okay, I'll stick my neck out...thinking outside of the box. 

CPVC is not listed for dry pipe use...but why?
(1) is this for just overhead piping where the water in pipe of a wet-pipe 
system will help keep the pipe from failing during a fire?
(2) or is this because air and CPVC are not compatible?
(3) or because the air will leak out thru the CPVC?
(4) some other unknown reason?

CPVC is listed for underground use...so why not use the CPVC if reason (1) 
above is the only problem. I don't know why CPVC is not listed for dry pipe 
systems, and I'm not the AHJ on this project...so I'm just wondering out loud.

rick matsuda, city of dallas, bldg insp dept

>>> [EMAIL PROTECTED] 04/17/07 04:05PM >>>
I've got a outdoor amphitheatre that needs sprinkler protection.  The
only option allowed to get from the controls (adjacent heated building)
to the arch on the amphitheatre is to go underground.  We will be using
galvanized pipe for the dry system for the amphitheatre.

The question is what pipe should I spec for the dry underground?  Can
(should) I use galvanized?  Do you sleeve it?  Any other suggestions?

Thanks,
Reed Roisum
Fire Protection Technician
Ulteig Engineers, Inc.
3350 38th Avenue South
Fargo, ND 58104-7079

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to