A door is NOT required. I can state this with certainty because I submitted a comment arguing that a door was needed on bathrooms. I argued that it should have a high level of separation than that for typical compartment since we are EXCLUDING protection. The committee REJECTED it and said follow the compartment rules. See ROC 13-282.

Greg - Let me know if we need to fax you a copy.

Roland

On Apr 26, 2007, at 11:42 AM, Greg McGahan wrote:



NFPA #13 2007 edition

A.3.3.2 Bathroom. A room is still considered a bathroom if it contains just a toilet. Additionally, two bathrooms can be adjacent to each other and are considered separate rooms, provided they are enclosed with the required
level of construction.

I have an AHJ that is stating that this excerpt from NFPA #13 is requiring a toilet room to have 20 minute walls to be considered a separate room with a
UL listed door.

Has anyone researched this? Is this the intent in 13?

Thanks,
Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:Sprinklerforum- [EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:Sprinklerforum- [EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to