I personally don't like heat tape as the "Freeze Protection" however that
being said, "Who would know?" The Owner, The Fire Dept. The Sprinkler
Contractor The alarm company and more. True this would only be after a
freeze and break, so the alarms sounded, but this doesn't seem a whole lot
different than what we see all the time with owners,"Guessing that it will
stay above freezing in a particular area" And then there is the contractors
out, "Owner shall maintain space at 40'F" of course if your putting heat
tape on the pipe, there's a pretty good indication that the owner doesn't
intend to keep it at 40'F.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Monday, May 07, 2007 8:08 AM
Subject: RE: Electric Heat Tracing - Background
The other issue is that fact that these systems were not supervised. A
break in the line at any point would render the system beyond that point
inoperable and who would know? If the system didn't function at all,
who would know? No way to insure operability.
Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Monday, May 07, 2007 9:11 AM
To: [email protected]
Subject: RE: Electric Heat Tracing - Background
Past conversations with NFPA and others informed me that heat trace was
originally prohibited due to the thought that it could fuse the
sprinklers.
NFPA admitted that to their knowledge heat tape had never done fused a
sprinkler and they were aware that there was a lot of heat tape in
service on branchlines throughout the country.
We just did a job where we used Chromalox products and learned a great
deal.
It is supposed to be around 100 deg max but under the worst conditions
it will not exceed 150 deg. We are only using 3 watts per foot however
and the temp varies accordingly from what I understand.
We have used it once before and had no trouble whatsoever.
Greg
Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dave
Phelan
Sent: Saturday, May 05, 2007 7:59 PM
To: [email protected]
Subject: Electric Heat Tracing - Background
Hello again all,
Im looking for the wisdom and experiences off the list for projects that
used electric heat tape for freeze protection. I currently have a
13R-2002 (metallic piped) project where the owner is looking to use the
Raychem XL Self Regulating heat trace for supplemental freeze
protection. The piping will be insulated as per the code but they want
a belt and suspenders.
Im looking for the code background as to why the appendix specifically
prohibits branchlines - rather forceful language I thought to be in the
appendix and not the code itself but oh well. The project natually is
looking to heat trace the crossmains and branches up to the drops for
the concealed pendants in the living space, hence my concern.
The product is reportedly listed UL for Fire Protection piping but I am
still awaiting all of that submission, in the mean time I need to
educate myself as to the why's and why not's in the code and branchline
prohibition.
Thank you once again.
Dave P.
An AHJ in New Jersey
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)