I believe it would push you to a full 13 system. From the 2003 IBC:

506.3 Automatic sprinkler system increase. Where a building is equipped
throughout with an approved automatic sprinkler system in accordance with
Section 903.3.1.1, the area limitation in Table 503 is permitted to be
increased......

When it says per 903.3.1.1, that section references NFPA 13. If it would
have added 903.3.1.2, that would be a 13R. Some section allow both 13 and
13R but this increase only allows a 13 system for the trade off.

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
www.burtellfire.com

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ken Holsopple
Sent: Monday, May 21, 2007 8:36 AM
To: [email protected]
Subject: IBC 2003 & 13 vs. 13R


Dear forumites,

I have an independent living facility that has three of the four floors that
are in excess of the 12,000 sq. ft. (+/- 17,000 sq. ft) limit established by
Table 503. The architect specified NFPA 13R as the design standard.

The use group is R-2 and the construction type is VA.

If an area increase is taken due to frontage (hence the 17,000 sq. ft.),
would that automatically push this into a full NFPA 13 system?

Best Regards,
Ken Holsopple
Design Manager 
Rowe Sprinkler Systems, Inc.
570-837-7647

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to