Hello Ken, Monday, May 21, 2007, 10:36:17 AM, you wrote:
KH> Dear forumites, KH> I have an independent living facility that has three of the four floors that KH> are in excess of the 12,000 sq. ft. (+/- 17,000 sq. ft) limit established by KH> Table 503. The architect specified NFPA 13R as the design standard. KH> The use group is R-2 and the construction type is VA. KH> If an area increase is taken due to frontage (hence the 17,000 sq. ft.), KH> would that automatically push this into a full NFPA 13 system? No. 13R would be applicable. The frontage increase is "slightly" independent of the requirement for sprinklers. A 5A, R2 building is limited to 12,000 sf per floor and a height of 50 feet or 3 stories. 504.2 allows ancrease to 60 feet or 4 stories. 506.1 allows you to get to 17,000 sf. for the largest floor. Then 506.4, Exception 2 allows an area increase for 13R buildings to 17,000 sf x 4 stories or a whopping 68,000 sf total building size (total of all floors.) Not my favorite section of the code. Often overlooked for limiting the size of buildings, but not in this situation. -- Best regards, Daniel Kaczor, Plans Examiner [EMAIL PROTECTED] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)