The area increase for frontage is not tied to sprinkler protection being provided.
Ray Schmid -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ken Holsopple Sent: Monday, May 21, 2007 10:36 AM To: [email protected] Subject: IBC 2003 & 13 vs. 13R Dear forumites, I have an independent living facility that has three of the four floors that are in excess of the 12,000 sq. ft. (+/- 17,000 sq. ft) limit established by Table 503. The architect specified NFPA 13R as the design standard. The use group is R-2 and the construction type is VA. If an area increase is taken due to frontage (hence the 17,000 sq. ft.), would that automatically push this into a full NFPA 13 system? Best Regards, Ken Holsopple Design Manager Rowe Sprinkler Systems, Inc. 570-837-7647 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)