Craig,

This was the first thought I had but that still leaves you with a damp
and humid environment. In fact, as the compressor replaces leaking air
sans moisture, the damp, humid environment should be enhanced. This
explanation then accounts for freezing, but so would 40 degrees F, but
not corrosion, so I don't see where 130 degrees F influences the need
for galvanized or not. No science here, just random thoughts so I'm
prepared for refutation

On 5/21/07, [EMAIL PROTECTED] <[EMAIL PROTECTED]> wrote:
More than likely they consider the temps above 130 capable of
evaporating any condensation or other moisture within the piping, thus
reducing the probability of corrosion and negating the need for the
galvanized pipe.




Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dee
Lockwood
Sent: Friday, May 18, 2007 6:16 PM
To: [email protected]
Subject: Galvanized sprinkler pipe at 130F

Has anyone experience with accelerated corrosion of hot dipped sprinkler
pipe used in a dry pipe system?

My application is galvanized pipe on a dry pipe system protecting an
attic that will see temperatures of 130F for a few hours a day and a
month or so each year.

FM Global Data Sheet 2-8N, 3-2, requires galvanized pipe in dry pipe
system "except where ambient temperatures exceed 130F." Section 2-3.1
references a lumber dry kiln. Obviously the operating conditions vary
greatly between an attic and a dry kiln. The chemistry in a dry kiln is
probably very complex.

I contacted the American Galvanizing Association. They are unaware of
any accelerated corrosion at 130F and feel galvanizing is stable to
350F.

Thanks

Dee Lockwood P.E.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to