Even though the 1 inch pipe does not seem to increase the gridding effect,
it still must be provided in the hydraulic calculations where it can end up
show some surprising effects.

Thank You

Rahe Loftin, P.E.
Region 7 - GSA
Office - 817-978-7299
Fax - 817-978-8644
Cell - 817-371-3102



                                                                           
                                                                           
             "Matthew J.                                                   
             Willis"                                                    To 
             <[EMAIL PROTECTED]         [email protected]    
             fp.com>                                                    cc 
             Sent by:                                                      
             sprinklerforum-bo                                     Subject 
             [EMAIL PROTECTED]         RE: Gang Drain for Attic Dry System 
             er.org                                                        
                                                                           
                                                                           
             06/28/2007 09:32                                              
             AM                                                            
                                                                           
                                                                           
             Please respond to                                             
             [EMAIL PROTECTED]                                             
              resprinkler.org                                              
                                                                           
                                                                           




Yes... But see 8.15.2.5.3.4 (02). The handbook gives a good commentary if
available. The piping is limited to 1", so you do not increase the gridding
effect.

R/

Matt

Matthew J. Willis
Living Water Fire Protection, LLC.
1160 McKenzie Rd.
PO Box 877
Cantonment, FL. 32533
850-937-1850 Voice
850-937-1852 Facsimile
[EMAIL PROTECTED]


----- >-----Original Message-----
----- >From: [EMAIL PROTECTED]
----- >[mailto:[EMAIL PROTECTED] On
----- >Behalf Of [EMAIL PROTECTED]
----- >Sent: Thursday, June 28, 2007 9:24 AM
----- >To: [email protected]
----- >Subject: Gang Drain for Attic Dry System
----- >
----- >
----- >This question was just posed to me by my Branch Manager -
----- >
----- >In an attic dry system with each branch line ending in
----- >what amounts to a "low?point", if the designer
----- >interconnected each branch line to?a 1-inch gang drain,
----- >would that not, in effect, create a gridded dry system?
----- >
----- >Ray Hoshall
----- >Service Manager
----- >FIRE TECH SERVICES, INC.
----- >
----- >_________________________________________________________
----- >_______________
----- >AOL now offers free email to everyone.  Find out more
----- >about what's free from AOL at AOL.com.
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to